Results 1 to 3 of 3
  1. #1

    Trane Comfort-R & CFM Setting

    I've seen the note on the Comfort-R guide that recommends against enabling Comfort-R if the cooling CFM/ton is below 400. Can anyone explain why?

    Thanks!

  2. #2
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    I'm going to take a guess and say that there would be a potential for the evap coil freezing up because of insufficient air flow.

  3. #3
    Quote Originally Posted by gary_g View Post
    I'm going to take a guess and say that there would be a potential for the evap coil freezing up because of insufficient air flow.
    I was assuming that it had something to do with the coil freezing or pressures or something....but the fact that it was a "recommendation" instead of a "you shouldn't do this" made we wonder if it's actually about efficiency or something else. :-)