Are we to assume that you installed this system yourself?
If you didn't, then you should be calling the installing contractor back if you have concerns about the TSP the control is showing.
Either way you've just found out first hand one of the first basic rules of air flow in ductwork. Velocity increases static pressure.Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.
-
06-18-2008, 10:05 AM #15
Regular Guest
- Join Date
- Jun 2008
- Location
- Perry Village, Ohio
- Posts
- 164
-
06-18-2008, 10:31 AM #16
Regular Guest
- Join Date
- Jun 2008
- Location
- Perry Village, Ohio
- Posts
- 164
-
06-18-2008, 10:37 AM #17
If its a VS blower. They don't always increase when you decrease the return.
-
06-18-2008, 10:44 AM #18
Regular Guest
- Join Date
- Jun 2008
- Location
- Perry Village, Ohio
- Posts
- 164
, I didn't decrease the return, I increased it (or are you talking about the pressure?) When I say I increased it, I mean I added more air to it by opening the blower door.
Also, when you say VS blower, do you mean a blower that a tech can jumper to adjust the blower speed or something that is controlled through some sort of circuitry that will increase or decrease the speed. In my case, the blower has to be jumpered (or whatever you guys call it).
Personally, I think there is something in the supply side either before or after the cooling coil. I have a call into a different servicing company that will do the annual maint on the unit. My Dad really recommended them as he has used them numerous times for when he builds his YMCA Dream homes. I'm thinking something is up there and hopefully they can fix that when they do their maint. Either that or the cockamamie way they have all the supply lines coming off the main trunk right after it leaves the furnace is the problem. Either way, I'm not sure how much that will cost, but it should pay for itself with added comfort and hopefully reduced bills.
-
06-18-2008, 10:48 AM #19
I was talking pressure.
VS blower are adjusted by jumpers/dip switches.
-
06-18-2008, 10:59 AM #20
Professional Member*
- Join Date
- Jul 2000
- Location
- Northern Wisconsin
- Posts
- 1,566
-
06-18-2008, 11:15 AM #21
Regular Guest
- Join Date
- Jun 2008
- Location
- Perry Village, Ohio
- Posts
- 164
-
06-18-2008, 01:32 PM #22
Professional Member*
- Join Date
- Jul 2000
- Location
- Northern Wisconsin
- Posts
- 1,566
Yes in varying amounts depending on all the different variables.
It increases the static pressure (between the air mover and the animal) because there is something causing resistance to air flow.
Air flows through ductwork basically the same way water flows through a garden hose. Go outside and experiment.Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.
-
06-18-2008, 01:42 PM #23
Regular Guest
- Join Date
- Jun 2008
- Location
- Perry Village, Ohio
- Posts
- 164
-
06-18-2008, 01:56 PM #24
Professional Member*
- Join Date
- Jul 2000
- Location
- Northern Wisconsin
- Posts
- 1,566
Now you're getting the general idea.
Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.
-
06-18-2008, 02:02 PM #25
Professional Member
- Join Date
- Jun 2006
- Posts
- 294
Where is this reading or readings taken? Is it the ESP or is it the pressure in the duct downsream of the blower. If it is the latter then the .1" increase is not surprising. You blow more air, then the static pressure in that duct will increase and since you opened the input, the suction side negative pressure will numerically decrease, resulting in a net lowering of the ESP.
Finallly, I am not convinced you have to do anything. What is your problem with the current system that would be lead you to make a correction? Is it noise or power?