Stack effect question
Would running a furnace/AC blower constantly or on an timed intermittant basis
reduce the pressure differentials in a dwelling caused by the stack effect?
-
06-13-2008, 10:32 AM #2
Only if by doing so, the running system pressurizes the house sufficiently so air is escaping through the building envelope vs. entering it. That can be accomplished by a fresh air intake on the return side of the system, but if you live in a humid climate, you'll load the house with moisture during compressor off cycle times and the indoor blower running. This can also occur if your return ducts/plenums are not in the air conditioned space, and are leaky.
Best way to reduce stack effect is to reduce leaks in the building envelope. Cheaper than running a blower, also.