    American Standard matched system ?

    Just checking to see if these two are compatable ? A/S 15 Seer #2A6H5022A1000A ... and ... A/S A/H #TWE031E13FB2 ?

    Also...... using a 4.80kw Auxiliary Heat strip what size breaker should be used at the main panel ? ...30amp?...40amp?

    thanks...paul

  2. #2
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,374
    Post Likes
    That's the old air handler model nomenclature. Unless it's an old model (in which case I couldn't tell you if it's a match or not), the model number should read 2TEE3F31A1000A. The heat pump model number should also be 2A6H5024A1000A (likely a transcription error). Have you considered R-410a equipment instead (you could get greater heating performance).

    Usually it's 30 amps for every 5 kW of heat strips. Better check with someone else here to be sure, though.

  3. #3
    Join Date
    Mar 2006
    Location
    The South
    Posts
    2,609
    Post Likes
    Bpawb

    that appears to be AmStd's Heritage 15 HP in a two ton R-22 configuration that has been discontinued.

    here are the performance numbers from the AHRI HP Directory.

    1106215 Discontinued Systems HERITAGE 15 AMERICAN STANDARD, INC. 2A6H5024A1 2TEE3F31A1 25000 13.00 15.10 22600 8.05 14100 1 HRCU-A-CB

    1106217 Discontinued Systems HERITAGE 15 AMERICAN STANDARD, INC. 2A6H5024A1 2TEE3F37A1 25000 12.70 15.00 21600 8.60 13200 1

    good numbers except for the poor HSPF eff. the larger air handler has better HSPF eff.

    here is an active configuration in the R-410a refrigerant.

    1382159 Active Systems HERITAGE 15 AMERICAN STANDARD, INC. 4A6H5024A1 4TEE3F39A1 25000 13.00 16.00 24000 9.00 13800

    very good numbers...

    IMO