    compressor failure

    hi everyone

    work on 2 ton goodman unit lo 65 HI 300 A 93* indoor 104*
    suc line never get cool or sweat vent put out 70* only, for all night.
    recovered ref and pulled vacuum to 30 M , for about about an hr.
    still got no relieve .
    checked metering device which is fixed ,and cut the line set and blowed opposite directions of eva coil seems good. nothing restricted.

    in the next morning suc line and eva coil frozen up a little .
    replaced eva coil,and it still dont solve the problem.
    cond and eva coil is cleaned. pressure remain same.

    so i replaced the condenser today ,and everything doing excellent as it should and expected .
    in my opinion suction valve in the comp was bad ,or is there any better way to tell if the compressor is goes bad ?

    any comment will be appriciated, thanks.

  2. #2
    Join Date
    May 2007
    Location
    Arizona
    Posts
    45
    LOL

  3. #3
    Join Date
    Apr 2008
    Location
    Rochelle Il / Chicago
    Posts
    169
    sound kinda like what I came accross today, Read my post "problem child"
    Goofy compressor

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,125
    A new LLFD would have been cheaper, and quicker.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Mar 2008
    Posts
    16
    Don't see how the suction valve could cause low suction press.

  6. #6

    compressor failure

    i did change the new LLFD twice ,i did't seem make a different after 1 hr.

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,125
    Did you remove the old one from inside the cabinet.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Just throw parts at it.

  9. #9
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,125
    He did, he already changed out the condenser.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Quote Originally Posted by beenthere View Post
    He did, he already changed out the condenser.
    And the evaporator...sounds like a new unit, darn near.

  11. #11
    Join Date
    Nov 2004
    Location
    North Carolina
    Posts
    443
    LMAO ! Well, he does still have the old air handler. Reckon that will be next if it ain't fixed now?

  12. #12
    Join Date
    May 2008
    Location
    Clovis/Fresno CA
    Posts
    254
    if you have to replace the evap and cond, you should have got a new E.E unit.

  13. #13
    Join Date
    Nov 2004
    Location
    Texas
    Posts
    9
    Did u check amp draw on comp to see what comp was doing? CHECK SH AND SC READINGS?
    300 HP AND 65 SUCT HOW WAS COMP BAD? JUST ASKING

    WAS THERE SUCT VALVE U COULD VALVE OFF TO SEE IF COMP
    PUMPS DOWN

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event