    I have a home that was built in the 60's. It has hydronic heat. About 8 years ago I added a air handler with central air.

    The unit is 10 SEER.

    Q1. Should I leave it alone and just pay the high electric bill?

    Q2. Replace it with a heat pump?

    Q3. Go all the way to geothermal?

    Thanks

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,760
    Its a shame to pull a perfectly good wotking A/C just to save a few bucks in cooling mode.

    You may want to consider pulling it, and replacing it with a heatpump with a hydro coil as your aux heat.
    That way, when the heat pump can't heat the house by its self, teh boiler comes on to help, but your still saving money on your oil, because teh heat pump is still running.
    It would be a dual fuel heat pump. Might cut you oil consumption in half.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Jan 2002
    Location
    East Grand Forks, MN
    Posts
    1,373
    It has hydronic heat. About 8 years ago I added a air handler with central air.

    The unit is 10 SEER.

    Q1. Should I leave it alone and just pay the high electric bill?

    Q2. Replace it with a heat pump?

    Q3. Go all the way to geothermal?

    Nothing wrong with a 10 SEER unit that is operating at the highest efficiency possible!

    My Questions:
    Q1. does the AHU have resistive heat?
    Q2. how does the hydronic get heated? fossil fuel or electric?
    Q3. are you willing to pay lots for geothermal system?

    Please answer these first!

    Al

  4. #4
    Join Date
    Apr 2001
    Location
    Lowellville Ohio
    Posts
    144
    Quote Originally Posted by arc8 View Post
    Nothing wrong with a 10 SEER unit that is operating at the highest efficiency possible!

    My Questions:
    Q1. does the AHU have resistive heat?
    Q2. how does the hydronic get heated? fossil fuel or electric?
    Q3. are you willing to pay lots for geothermal system?

    Please answer these first!

    Al
    A1. Yes, but very seldomly used. Only when problems with boiler.
    A2. Fuel Oil
    A3. At 57 years old, I'm not sure I will see the payback. At $4.00+ for oil and a yearly consumption of 450 gallons I'm just trying to save money.

  5. #5
    Join Date
    Jan 2002
    Location
    East Grand Forks, MN
    Posts
    1,373
    Does your utility company offer off-peak or reduced rates for dual sources of heat?

    If yes, maybe you should install an electric boiler with either an LP boiler or higher eff oil boiler!!!

    Al

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,760
    The heat pump will off peak rates still be cheaper to use then an electric boiler with off peak rates.

    A high efficiency boiler may only reduce his oil consumption by 50 gallions. Long long time before ROI.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Jan 2002
    Location
    East Grand Forks, MN
    Posts
    1,373
    PGPGSR

    If you could live with a HP heating your house instead of an hydronic system, then do it.

    But, i did not measure your house, so i can not suggest the best system for your annual operating cost!

    Al

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,760
    450 gallions of oil current consumption. New high efficiency boiler, if it cuts his consumption by 35%, 157 gallions. 8 years to break even at current oil cost.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Apr 2001
    Location
    Lowellville Ohio
    Posts
    144
    Quote Originally Posted by beenthere View Post
    450 gallions of oil current consumption. New high efficiency boiler, if it cuts his consumption by 35%, 157 gallions. 8 years to break even at current oil cost.
    I have what was considered a high efficency boiler 20 years ago. It is a Burnham V1-96. I thoroughly clean it every year.

  10. #10
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,760
    Quote Originally Posted by PGPGSR View Post
    I have what was considered a high efficency boiler 20 years ago. It is a Burnham V1-96. I thoroughly clean it every year.
    So just getting a higher efficiency oil boiler is a waste of money.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Apr 2001
    Location
    Lowellville Ohio
    Posts
    144
    Quote Originally Posted by beenthere View Post
    So just getting a higher efficiency oil boiler is a waste of money.
    In my opinion also. That is why I am contemplating a heat pump or geothermal. I think that I have ruled out simply getting a higher SEER A/C. But that way I wouldn't have to replace the air handler.

    By the way, my Wife has COPD so my A/C is on from April until October.

  12. #12
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,760
    With a heat pump, get everything new. That way, full warranty on everything.
    And have a hydro coil installed to use your oil as aux heat.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event