    Carrier Infinity 19 Or 16 Heat Pump

    Manual J test shows a 4 ton unit for my home. I live north of Dallas and have a 2000sq feet home. My home is tight and has high celings. The difference in price is not that much. I want to purchase the best system to cool my home and remove the humidity. I thought I read once that the 16 seems to remove more humidity? Any thoughts or which route I should go? I will also replace all the ducts and add another return.

    Kirk

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,765
    For humidity control the 16.

    Its system capacity in first stage should be around 2.4 tons.
    The 19's first stage capacity will be around 3.2 tons.

    So the 16 will have the longer run time in first stage.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    The 19 is still much better at dehumidification then your old unit and higher SEER.

    In Houston the 16 for dehum. ,not sure which in Dallas.

  4. #4
    Join Date
    Mar 2006
    Location
    The South
    Posts
    2,148
    kirk

    here are the AHRI performance numbers using same air handler.

    1250419 Active Systems INFINITY 16 PURON HP CARRIER AIR CONDITIONING 25HNA648A30 FE4ANB006+UI 48000 11.80 16.30 47500 9.30 27800

    1158713 Active Systems INFINITY 19 PURON HP CARRIER AIR CONDITIONING 25HNA948A30 FE4ANB006+UI 46500 12.60 16.80 48000 9.30 26800

    as you can see, not a big difference and for hot humid Texas, the Infinity 16 may be your best bet. I am not real clear of the major differences other than the type compressor and the low stage. with rebates involved, are the prices close? you will note a little higher cooling BTUs with the 16.

    IMO

  5. #5
    Join Date
    Apr 2006
    Posts
    81
    Quote Originally Posted by tigerdunes View Post
    kirk

    here are the AHRI performance numbers using same air handler.

    1250419 Active Systems INFINITY 16 PURON HP CARRIER AIR CONDITIONING 25HNA648A30 FE4ANB006+UI 48000 11.80 16.30 47500 9.30 27800

    1158713 Active Systems INFINITY 19 PURON HP CARRIER AIR CONDITIONING 25HNA948A30 FE4ANB006+UI 46500 12.60 16.80 48000 9.30 26800

    as you can see, not a big difference and for hot humid Texas, the Infinity 16 may be your best bet. I am not real clear of the major differences other than the type compressor and the low stage. with rebates involved, are the prices close? you will note a little higher cooling BTUs with the 16.

    IMO
    Since the 16 has a higher cooling BTU does that mean it cools better?

    Kirk

  6. #6
    Join Date
    Mar 2006
    Location
    The South
    Posts
    2,148
    Quote Originally Posted by kkmcewen View Post
    Since the 16 has a higher cooling BTU does that mean it cools better?

    Kirk
    cool better? humm..

    in most cases, probably not. however, if your cooling load is borderline , then the additional 1500 BTUs might be helpful. But that's only an extra 3.25% above the 46,500. I would want it for Texas summers.

    IMO

  7. #7
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Quote Originally Posted by kkmcewen View Post
    Since the 16 has a higher cooling BTU does that mean it cools better?

    Kirk
    48,000 - 46,500 = 1500 more btu per hour.

    The 16 is a true 4 tons (48,000 btu). Couple this with the lower first stage capacity, I would answer "Yes, it should cool better for your situation".

    Good luck.