    Quote Originally Posted by perrybucsdad View Post
    Thanks Dash.... I'll make sure someone does a static pressure test then. Does every contractor do them? From looking at this site it looks like some do and some don't. From what you said it would indicate to me that this would tell the contractor if the ductwork is adequate or not. Maybe that is an oversimplified explanation, but that's what I am getting from your post.
    Static pressure .taken correctly,along with the manufacturer's "fan Data chart" information used correctly will give you the cfms for the motor speed it was running on at the time it was taken,

    Good idea to have the fan data there when the test,so they can change the speed if needed and retest.

  2. #41
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Quote Originally Posted by perrybucsdad View Post
    Festration... what the heck is that?
    The opposite if Infestration

  3. #42
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    Fenestration, Glazing, Windows. Same thing.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #43
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    Quote Originally Posted by dash View Post
    Good idea to have the fan data there when the test,so they can change the speed if needed and retest.
    Where would I find the fan data? In the manual for the furnace?

  5. #44
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    Quote Originally Posted by perrybucsdad View Post
    Where would I find the fan data? In the manual for the furnace?
    Yes.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #45
    Join Date
    Oct 2003
    Location
    southern mo.
    Posts
    323
    is all the return drawn thru the walls? you most likely have a return problem,very common on new construction.

  7. #46
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    Hmmm... I see nothing in the install manual.

    BTW, the furnace is a Whirlpool 90+ Gas Furnace (Thought I had the model on here but I do not), and the outside compressor is w Whirlpool WC136A-1A. I tried looking on the Whirlpool website for that model of the compressor and they do not list it anywhere. That's scary.

    Anyone know anything about them?

  8. #47
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    You may not reconize the fan data section. Or its some what possible it doesn't have one.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #48
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    Beenthere... actually, I found it online. It was in a document that they did not leave (just like the compressor and the coil).

    Now I see how important the static pressure data is. Since I don't have the exact model number to tell me more about the airflow descriptor, I can't say for certain what CFM I should be seeing, but I can see a that it can go from 2070 CFM @ .20 SP to 1570 CFM @ .90 SP. Wow!

    So what exactly is static pressure? Is it how much suction or resistance the blower is having to overcome on the return air side?

    One thing I tried last night was to see if the main cover over the bower would get sucked back to the unit if I tried to remove it. When I removed it, it did not want to come off the unit with the blower running. I ran it without the cover for some time last night and I could notice a marked improvement in air output in the far room. Not blasting air, but still a good breeze compared to what we had seen. I think that would tell me that there is an air delivery problem.

    One other thing I noticed while running it this way, was that the door to the basement behaved strangely. Normally, I can sort of close the door so that it is just cracked and it would stay that way. While I had it running with the cover off, the door would open at a medium speed. Is this part of that static pressure?

    Well, anyhow, I placed a call this morning to a different HVAC contractor who is going to come out this afternoon to take a look at it. He said he would perform a static pressure test for me, which is good. My neighbor (who is not an HVAC guy) said he had the equipment to do it, but when he said he would be drilling into my furnace, I told him I would rather wait for a professional to do it. I understand that you need to drill into it, but I would feel quite a bit more comfortable if a pro did it.

  10. #49
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    The static pressure is a measurement of resistance that the blower is working against in both the return and supply. Although they are measured seperately, they are added together to get the total static pressure.
    Yours could be more then .9"
    The contractor can get the model number of your unit, and you may be able to find the correct chart for your unit online then.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #50
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    So how would they lower my static pressure? More returns?

    r22jjc... yes, all of my returns run in the walls.

  12. #51
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    Could be more returns. Larger grilles. Larger return ductwork. Add more return duct.

    Good chanc a combination of the above.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #52
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    Could it be resistance in the supply lines? Maybe the trunk is too small?

    I took a look at my neighbors system last night (different builder and very efficient). His house he can drop the temp fairly quickly. His supply and return lines looked very simple. None of his dampers were engaged and he had nice and strong delivery in all rooms.

    Mine on the other hand takes all kinds of turns etc.

    I also just talked with my builder this AM. I was surprised that he said he would get a contractor out there to fix it. He mentioned something about adding fans to the supply lines to help push the air to the farther rooms. From reading on this site, it sounds like most of you do not favor that. And if in fact my static pressure is quite high, I would think there has to be a way to decrease it which would help with my utility bills (my electric bill is almost twice what my neighbors is and he keeps his house cooler than I do).

    Since I brought this up during my homeowners warranty period, and the builder said he would fix it, am I within my right to demand that a certain static pressure (within reason) be archived? If so, what should my target be?
    Last edited by perrybucsdad; 06-12-2008 at 09:29 AM. Reason: addition...

Page 4 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event