  1. #66
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,038
    Yes, individual readings will tell which one has the most trouble.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #67
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    Okay... just out of curiosity though, in an ideal system, would both numbers be the same?

  3. #68
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,985
    This thread has been very interesting.

    He could & should have done a lot more pressure drop checking to pinpoint where all of the excessive pressure drops across areas are located.

    The ESP when checking before blower - RA side - & before entry to the A-Coil could even be low & airflow could still be low, in that case you would check for major duct leaks on the various runs, or lint clogged blower wheel blades, etc.

    A combination of major duct air-leaks & restrictions might leave you with a good looking .4" to .5" ESP, & low airflow, which calls for a tech that knows how to troubleshoot a duct system.

    http://www.udarrell.com/external_sta..._readings.html
    - udarrell
    Last edited by udarrell; 06-13-2008 at 12:50 PM. Reason: Stating where probes need to be for ESP reading

  4. #69
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,038
    Quote Originally Posted by perrybucsdad View Post
    Okay... just out of curiosity though, in an ideal system, would both numbers be the same?
    In ideal land, they would be. In our world, they won't be.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #70
    Join Date
    Jun 2008
    Location
    Perry Village, Ohio
    Posts
    164
    Thanks for the great link udarrell.

    In reading your link, I keep seeing things about duct leakage. I can understand this on the supply side, but do I need to worry about that on the return side?

Page 6 of 6 FirstFirst 123456

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event