Page 1 of 6 123456 LastLast
Results 1 to 13 of 71
Thread: True or False?
    Jun 2008
    Wisconsin, USA
    True or False?
    True or False... Air leaving the evaporator coil is at 100% humidity
    Western NC
    false
    Close to 100% relative humidity.
    Jun 2008
    Wisconsin, USA
    LOL this is a true or false question
    Western NC
    yeah anyhow
    Toledo, Ohio, United States
    Twilli say true
    No Heat No Cool You need Action Fast
    Rapid City, SD
    False... if you're running the furnace (no A/C) there's no way it could be
    Jun 2008
    Wisconsin, USA
    (At Least) one wiseguy in every crowd... let's assume its summertime and its 75 degrees and 55% relative humidity in the house and the A/C is running with an evaporator temperature of 45 degrees.
    True or False... Air leaving the evaporator coil is at 100% relative humidity
    Western NC
    whats the pressures?
    whats the refrigerant?
    How many people in the home?
    Whats the family dogs name?
    until these are verified......can't give you an honest answer.
    Aug 2005
    San Diego,CA
    I say false...I could be wrong though...
    Sink or Swim!
    A Man has to know his limitations..
    To be old and wise, one must be young and dumb..
    Grundy Co. IL
    Or you maybe right 50/50, gotta love true or false, I think that's how I made it through high school.
    Jun 2008
    Wisconsin, USA
    In order to remove moisture from the air, the air must be cooled below
    the dewpoint. For example 75 degree air entering a 45 degree evaporator
    coil at 55% relative humidity and exiting the evaporator at 55 degrees.
    The air is now below the dewpoint so the wet bulb and dry bulb temperatures
    are the same... If the wet bulb and dry bulb temperatures are the same,
    you are also at 100% humidity.
    The answer is True
    Bypass factor
    never seen wb and db temps the same exiting the evap
    Your theory would be correct if you could have 100% of the air move across the surface of the coil.