Results 1 to 10 of 10
    Atlanta, Ga
    Too many returns?
    Could too many returns on a unit be a bad thing? I was asked this question but never thought about it before?
    Joe
    No
    Jul 2001
    VA
    Only in terms of money .....at some point I would think they won't help anymore If grossly overdone, but do cost more.
    Jan 2002
    East Grand Forks, MN
    Never heard of it!
    Houston,Tx.
    Quote Originally Posted by Joe Mascitti View Post
    Joe
    If there all fresh air returns you could have an issue or two.
    Dallas & Longview, TX
    I'd think that if they are in unconditioned space, the more you run would also increase heat gain/loss as the smaller ducting for multiple runs would have more conditioned air exposed to the heat/cold. Secondly, the more connections the more chance of a leaky seal both in the return grill and plenum? Unless you leave doors open then you have pressurization issues or jumpers that probably balance the loss though.
    Dec 2006
    Dallas
    After the required return airflow is satisfied, excess returns in unconditioned space will add to undesired total heat gain / loss resulting in wasted energy.
    Sometimes extra returns are needed for zoning, which results in much less airflow from the inactive zone return, but as air travels at a low speed through the inactive zone's return, in unconditioned space it's arrival temperature at the AH is much higher / lower in the undesired direction. Not a huge factor, but it's a calculatable factor that discorages excessive returns...in unconditioned space.
    Total duct surface area / R value = Loss
    Oversized eturns,could result in very low static,which could result in more air flow then desired.Not likely but it could happen.
    That's what your MERV 20 is for.
    Quote Originally Posted by Daltex View Post
    That'll probably work!!!