    Unhappy Rooms with doors closed too hot or cold

    Got a nagging problem with our 5-ton Trane setup. It's a 3-zone system on an older split-level (three levels) cedar shake house. The thermostats are all in a hall area, which seemed like a good idea at the time of install. However, what happens is that when a bedroom door is closed, it'll get too hot because the thermostat is not in that room. My husband tells me that the only way to fix this is to install grills/vents in all the doors, but I'm thinking there has to be another way. After all, new homes don't have all the bedroom doors vented. I don't want the kids hearing what goes on outside the bedroom, nor do I want them to hear what goes on inside the bedroom. Are there any other options? Thanks very much.

  2. #2
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    Post Likes
    Instead of putting vents in the doors you can have your hubby undercut the doors a 1" or so off the bottoms of the doors will serve the same purpose as putting vents in the door's. By doing this will allow the air to move out of the bedroom when the door is closed and not get too hot or cold.

  3. #3
    Join Date
    Jun 2008
    Posts
    10
    Post Likes
    Thread Starter
    Thanks, DanW13. I appreciate your reply, but to me, that's about the same as putting a vent in the door insofar as hearing what goes on in/out of the bedrooms is concerned. I'm really curious about what new construction homes do if they don't have the doors vented or cut too high off the floor. Guess I'm hoping that some cool stuff can be done with thermostats or something like that.....

  4. #4
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    "Jumper returns" can be installed from the ceing of the affected room to the hallway or living area.


    Undercutting the door 1" would give you almost 30"s of free area ,with no grille restriction and less sound transmission then grilles in the door.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Done right. jumper ducts won't tranmit sound like an under cut door.

  6. #6
    Join Date
    Nov 2004
    Location
    Skokie , IL near chicago
    Posts
    1,197
    Post Likes

    r a problem

    Quote Originally Posted by bhe View Post
    Thanks, DanW13. I appreciate your reply, but to me, that's about the same as putting a vent in the door insofar as hearing what goes on in/out of the bedrooms is concerned. I'm really curious about what new construction homes do if they don't have the doors vented or cut too high off the floor. Guess I'm hoping that some cool stuff can be done with thermostats or something like that.....
    New construction that i've seen have a return in every room , except kit & bath of course , can u use joist spaces for returns at all????.......Jack

  7. #7
    Join Date
    Jun 2008
    Posts
    10
    Post Likes
    Thread Starter
    Thanks, rojacman, been there and dash.
    There is a return air in two of the bedrooms, but I'm sure that's not the same as a jumper duct. That sounds intriguing. We have joist or attic space available for all three bedrooms in question. Can anyone give me a little more detail on what a jumper duct is so I won't sound like the newbie I am when contacting an A/C professional? The guy who installed ours would only tell us to install vents in the doors, and I just thought there had to be other options. Thanks again.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Do those 2 bedrooms also have trouble cooling when the doors are closed?
    If so, the returns may be undersized.

    A jumper duct. Is when you install a register in the room, and then run a duct out to(in your case) the hallway. And attach it to either a register cut into the hallway, or into the return box in the ceiling above the hall.
    If the return in the hall has a filter in it, then your need to install return fiter grilles in the bedrooms.

  9. #9
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    A little while back I found this on building science and it talks about transfer grills

    "Transfer Grille
    From Builder’s Guide, Building Science Corporation
    • All supply registers should have clear access to a return grille in order to prevent the pressurization
    of bedrooms and depressurization of the common area. Bedrooms should either have hard-ducted
    returns, or another means of pressure relief, such as transfer grilles (above) or jump ducts (below).
    • Maximum that can be returned by through-the-wall hi-low transfer grille is ~125 CFM, assuming
    door undercut.
    Door undercut of 1” minimum still required
    • Pressurization is especially severe when combining oversized air handlers (e.g., 5 tons in 2000 sf)
    and large master bedroom suites that can be sealed from the main space with one door.
    Undercutting the door seldom provides adequate pressure relief.
    • Refer to Transfer Grille Sizing Table to compute required free area (and grille size) vs. supply airflow."



    I tried loading it up again and for some reason the doc. won't load up now it maybe my laptop.....it showed all the different types that these guys are talking about.

  10. #10
    Join Date
    Jun 2008
    Posts
    10
    Post Likes
    Thread Starter
    Wow, BigJon3475 - your post hit the problem right on the head. The bedroom I have the most experience with has a major problem with pressurization. When the A/C turns on, the door will close by itself if it's just a little ajar. And I believe we have too large of a unit - it's 5 tons for 2100 sq ft, 3 zones. (The force of the air upstairs, closest to the air handler, is incredible and I think we were misled into thinking we needed the larger unit, but that's another issue entirely). I found a website for buildingscience.com, is that where you got your info?

    Beenthere, yes, those bedrooms have trouble cooling when the doors are closed. You have to turn the thermostat down at least 3 degrees for that room to be as cool as the living area when the door is closed, and the living area then gets too cold, of course. The return air on the main bedroom, with the pressurizatino problem, is not too small - it's about 10X20.

    Thanks SO much.

  11. #11
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes

  12. #12
    Join Date
    Jun 2008
    Posts
    10
    Post Likes
    Thread Starter
    No go, Big Jon3475. I tried just looking for the Builder's Guide, but the links were to a place to purchase the Guide, not for info in the Guide.

    I guess I just need to find a good A/C technician. Unfortunately, the last one (that installed this system and it's ductwork) doesn't seem to know all there is to know, and referral from a layman is probably not going to be helpful. After all, our guy was really nice and honest and hard-working, but this issue requires more technical expertise than he had, apparently. Got a clue about how to find someone really knowledgeable?

    Thanks again.

  13. #13
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    If you have a zoned system you should have some sort of Barometric Pressure Relief Bypass Duct, if not you sure will be having issues with Pressurization in some rooms, unless you maybe have a dedicated return for all rooms, if your in a pretty humid area you could also get your tech to look at slowing down the CFM's to 350 per ton., or is this a VS air handler? not much was mentioned about equipment except it was a Trane system.
    Last edited by Mr Bill; 06-09-2008 at 05:13 PM.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  14. #14
    Join Date
    Jun 2008
    Posts
    10
    Post Likes
    Thread Starter

    Confused

    Thanks, Mr. Bill. Unfortunately, I'm just a layman and have no clue what a VS air handler is. I'm in Jacksonville, Florida, about as humid as you can get. Pressurization isn't the main problem, of course, I guess it's a side effect of what's causing the problem, if I'm understanding everyone correctly. What a helpful bunch of people you are.

  15. #15
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by bhe View Post
    Thanks, Mr. Bill. Unfortunately, I'm just a layman and have no clue what a VS air handler is.
    "variable speed" That means that the Air handler has a variable speed motor in it, most of these motors are able to overcome a lot of air duct issues that other fixed speed motors can't, by ramping up or down when needed, hope this helps.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  16. #16
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Quote Originally Posted by bhe View Post
    No go, Big Jon3475. I tried just looking for the Builder's Guide, but the links were to a place to purchase the Guide, not for info in the Guide.

    I guess I just need to find a good A/C technician. Unfortunately, the last one (that installed this system and it's ductwork) doesn't seem to know all there is to know, and referral from a layman is probably not going to be helpful. After all, our guy was really nice and honest and hard-working, but this issue requires more technical expertise than he had, apparently. Got a clue about how to find someone really knowledgeable?

    Thanks again.
    Try this;

    http://www.buildingscience.com/bsc/d...montgomery.htm

  17. #17
    Join Date
    Jun 2008
    Posts
    10
    Post Likes
    Thread Starter
    Thanks, dash and Mr. Bill. This is good information. Perhaps I can do a little more research on this and then (hopefully) find a good A/C guy that understands this stuff and can apply it to our situation. Any certifications or something like that to look for when trying to find someone?

  18. #18
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by bhe View Post
    Beenthere, yes, those bedrooms have trouble cooling when the doors are closed. You have to turn the thermostat down at least 3 degrees for that room to be as cool as the living area when the door is closed, and the living area then gets too cold, of course. The return air on the main bedroom, with the pressurization problem, is not too small - it's about 10X20.

    Thanks SO much.
    The grille may be 10 x 20, but what size is the duct thats hooked to it.
    In order for that room to pressurize, the supplies must be putting more air into the room then the return can take out.

  19. #19
    Join Date
    Aug 2006
    Location
    Marco Island, Fl
    Posts
    760
    Post Likes
    Please do a simple experiment before you have more grills and jumpers cut in, although proper air return and pressure equalization is essential to good operation.

    You see, you are not saying the rooms don't cool, just the hallway and living areas are cooler when the bedrooms are at their desired temperatures.

    Prop the doors in question open from the door frame the width of a shoe.

    Let them run for a day or so. If that solves your problem, jumpers and such may help.

    If the rooms are still hot, it may be a simple thermostat location issue.

    In new homes, and especially Master bedrooms, windows are prevalent. If the bedrooms rooms faces north east to northwest, a thermostat in the hall may not trigger on....especially with the doors closed. Hallways are generally toward the interior of the home, and bedrooms generally on the outer part of the home with external walls and windows. I find many times air from the other zones keep the thermostat off and satisfy it early. The living area part of the zone in question, may be getting help staying cool from other zones.

    Zone systems should try to be set up where similar loads are grouped together so this does not happen.
    Once the thermostat can sense the load properly, airflow can be balanced.

  20. #20
    Join Date
    Dec 2005
    Location
    San Jose, CA
    Posts
    465
    Post Likes
    move the thermostat to the bedroom

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •