He cleaned the condenser coil. The evap was clean (I'm careful about my filter maintenance!)
-cinergi
-
06-17-2008, 05:12 PM #15
OK, guys. Here's what I don't understand: it sounds like the system was building up head pressure and eventually the internal relief valve was venting back to suction side. This would continue until the internal overload in the compressor would finally kick out. After cooling off awhile, it would reset. My question is this: how would a bad TXV cause this to happen? Why wouldn't it just pump down, and cut out on low suction pressure? Or just continue to run into a vacuum? Why the excess head pressure?
-
06-17-2008, 06:00 PM #16
Or... is the TXV somehow sticking wide-open and causing the high head??
-
06-17-2008, 06:51 PM #17
Condenser may not be able to hold the entire operating charge.
-
06-17-2008, 08:17 PM #18
TXV could be hunting severly. Causing a constant change in pressures and temps.
I fully support the military and the War on Terrorism.
If you don't know, then don't do. If you don't know and still do, then be prepared to pay someone else a lot to undo what you did and then do it right.
If you do know, then do. But do it right. Otherwise, you may not be doing it long.
-
06-17-2008, 09:40 PM #19
Professional Member
- Join Date
- Mar 2003
- Posts
- 7,249
many resi units do not have low presssure switches.
-
06-17-2008, 10:16 PM #20
So where is all the heat coming from to elevate the Head pressure? If the low side is into vacuum it's not moving any heat from the evap. coil. All the refrigerant is stacked in the condenser and liquid line, being cooled down to ambient. Is it possible that the high compression ratios and the heat of compression are responsible for all the excessive head pressure? I've never witnessed a system running long term into a vacuum with no LPCO to know the effects this has.
-
06-17-2008, 10:18 PM #21
-
06-17-2008, 10:33 PM #22
Depends on line set and indoor coil match.
-
06-17-2008, 11:09 PM #23
Professional Member
- Join Date
- Jun 2008
- Location
- Surrey, BC, Canada
- Posts
- 35
I wonder if it's a R410A unit. With R22 I hardly ever ran into a TXV problem. Seems like more frequent failures with the R410A.
-
06-18-2008, 09:46 AM #24
Regular Guest
- Join Date
- Jan 2008
- Posts
- 40
It's an R-22 system, circa 1996. The tech said the same thing: he rarely has problems with the R-22 systems, but often replaces various sealed-system parts on the R-410 units because of the higher pressures.
-cinergi