    Contactor not pulling in

    Was scratching my head this afternoon. Replaced a PE switch for an Indeeco Duct heater. Calibrated thermostat, calibrated switch for when it sees 13psi of air the NO switch will close and send a 277 signal to my stage one contactor coil. Checked for continuity when the switch closed (13psi) before I applied power; good. Applied power, increased thermostat for full heat, stage 2 and 3 pull in but 1 doesn't. Manually pushed in stage 1 contactor , felt a slight bit of resistance but then it pulled in magnetically, stayed closed for a bit, had amp clamp on line side to heater and amps were within reason, then it opened. Cycled power, contactor made, then it broke. Decided to replace contactor. 2 pole, 30 amp, 277V coil. Wired it up exactly how it was and confirmed via schematic. Applied power with full heat call and nothing. Stage 2 and 3 close but 1 doesn't. Checked for potential across my PE switch 0. Check for voltage at coil ( coil terminal 1 and terminal 2 ) 0. Coil terminal 1 to ground 277, Coil terminal 2 to ground 277. Check the continuity of the wires all good. Any help would be great

  2. #2
    Join Date
    Jun 2013
    Location
    N. Canada
    Posts
    878
    Post Likes
    What's measured voltage ACROSS coil?

    Stop measuring to grnd, measure v across switches etc to find the under-load poor connection.

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    277 to ground?

    What PPE did you have at the time?

  4. #4
    Join Date
    Jun 2013
    Location
    N. Canada
    Posts
    878
    Post Likes
    Quote Originally Posted by pecmsg View Post
    277 to ground?

    What PPE did you have at the time?


    PPE?

    Post Partum Elation?

  5. #5
    Join Date
    Feb 2014
    Location
    Northern VA
    Posts
    6
    Post Likes
    Thread Starter
    voltage across the coil was zero as I had stated but didn't describe it well enough. This is a duct heater from 1989. all circuits are 277. line side and coil side.

  6. #6
    Join Date
    Jun 2013
    Location
    N. Canada
    Posts
    878
    Post Likes
    Is your coil #2 out returning to the wrong leg of 277v ?

    And you're sure there's NO v drop across actuation switch?

  7. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    I think it's right in front of you.

    You have zero across the coil, BUT you have 277 to "ground" on both sides. What does that tell you? It tells me that the common side of your coil is nearly open, has high resistance due to a bad connection, or there is a control in the common side that has high resistance.

    Your problem, either way, is in the circuit on the side of the coil that does not have the PE switch.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #8
    Join Date
    Oct 2013
    Posts
    327
    Post Likes
    Dumb question but is this three phase? I recently went round and round with a 220v pond pump and found out the voltage on the contactor coil, I was reading each side both from L1 and thought the contactor had voltage only to find that I had to have a jumper to the other L2 leg to make the 220v contactor work.

  9. #9
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by Deltashmelta View Post
    Dumb question but is this three phase?
    You get 277 volts from a 480 volt 4 wire Delta Y service. Any phase with the neutral will yield 277 volts.

  10. #10
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Even though voltage is high, it is exactly like how 120 volts' neutral is derived on a 208 volt three phase service. Except the service is derived from 460 volt, three phase. 277 volt is never three phase, one side is at zero potential.

  11. #11
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    There is a break somewhere between the coil and neutral...did they break neutral with a contact somewhere that is open?
    "If history repeats itself I am so getting a dinosaur"

  12. #12
    Join Date
    Feb 2014
    Location
    Northern VA
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by Hrdworkingacguy View Post
    There is a break somewhere between the coil and neutral...did they break neutral with a contact somewhere that is open?
    Every other switch within the circuits are closed , APS, manual and auto thermal cutout, and stage 2 and 3 heater contactors are closed and heating. those are all that is there.

  13. #13
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    277v coil is a 277v line on one side and neutral on the other. If you have 277 on one side, and no 277 when you go across the coil, and it doesn't pull in, then you don't have a path to neutral, period...

    Put one meter lead on neutral and work back to the coil, somewhere you will get 277v and that's your break.

  14. #14
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    I think someone else said that.

    Wait a minute, that was me.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  15. Likes VTP99, Bald Menace liked this post.
  16. #15
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    i love this site..
    Let's give nukes a chance.

  17. #16
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    I just said it in a different way after the op challenged our diagnosis.

    In all honesty I skimmed after the first couple posts..

  18. #17
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Pretty hard for a contactor to pull in with no potential on the coil.


    Quote Originally Posted by VAsteamfitter View Post
    Was scratching my head this afternoon. Replaced a PE switch for an Indeeco Duct heater. Calibrated thermostat, calibrated switch for when it sees 13psi of air the NO switch will close and send a 277 signal to my stage one contactor coil. Checked for continuity when the switch closed (13psi) before I applied power; good. Applied power, increased thermostat for full heat, stage 2 and 3 pull in but 1 doesn't. Manually pushed in stage 1 contactor , felt a slight bit of resistance but then it pulled in magnetically, stayed closed for a bit, had amp clamp on line side to heater and amps were within reason, then it opened. Cycled power, contactor made, then it broke. Decided to replace contactor. 2 pole, 30 amp, 277V coil. Wired it up exactly how it was and confirmed via schematic. Applied power with full heat call and nothing. Stage 2 and 3 close but 1 doesn't. Checked for potential across my PE switch 0. Check for voltage at coil ( coil terminal 1 and terminal 2 ) 0. Coil terminal 1 to ground 277, Coil terminal 2 to ground 277. Check the continuity of the wires all good. Any help would be great

  19. #18
    Join Date
    Jan 2008
    Location
    Phoenix Arizona
    Posts
    1,663
    Post Likes
    LoL seriously...He has power to the contactor, just not a complete circuit.

  20. #19
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by BBeerme View Post
    Pretty hard for a contactor to pull in with no potential on the coil.


    He has power, but he was using "ground" for that check.

    One side (the neutral) of the coil is not connected somewhere, so he can't read across the coil.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  21. #20
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by VAsteamfitter View Post
    Every other switch within the circuits are closed , APS, manual and auto thermal cutout, and stage 2 and 3 heater contactors are closed and heating. those are all that is there.

    Have you found the solution yet, or are you stumped? I can give you my number.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •