Results 14 to 21 of 21
    Jun 2008
    Wisconsin, USA
    Not enough data... Besides the condensing coil being clean, type of condensing coil (fintube or spinfin), size of condensing coil, heat load on dwelling (system properly sized), Correct system charge... There are so many variables that the question cannot be answered as asked.
    NW burbs of Detroit
    124* is damn close to flashing in the liq line.
    Quote Originally Posted by tonydykes55 View Post
    if a filter dryer is clogged would the line be hotter coming from the condenser and colder on the evap side and would it cause high head pressure?
    No, the condenser wouldn't be hotter, but the LLFD generally would be cooler on the evap side, And wouldn't raise head pressure that it would be overly high, unless the total charge was more then the condenser can hold, or the unit was over charged.
    NW burbs of Detroit
    Beg to differ Beenthere.If a restriction exists it could be severe enough to cause volume of suction gas returning to cool comp to be reduced.
    This can cause a superheated condition in condenser on a high load and ambient conditio.
    That would cause the compressor discharge gas to be hotter. But the refrigerant exisiting the condenser coil would not be.
    NW burbs of Detroit
    It can. Been on both residental and commercial jobs with press over 325psig
    and the gas can't be de-super heated so the condenser is blazing.
    Was the cause of the high pressure a clogged LLFD.
    NW burbs of Detroit
    Filter or bad txv jammmed partialy shut.