  1. #1
    Join Date
    Aug 2007
    Location
    Spartanburg, S.C.
    Posts
    58

    Hmm whats up with this?

    At a unit today, cust. says 6 yrs. old, one changed compressor nothing else ever serviced. He is just not comfortable in home( 96 yesterday) well bet no one has had this. 6 year old Tempstar outdoor unit pulling air from top and blowing out sides. Wow what a condensor temperature split. Anyway it was 9 45 so i have to go back today to investigate.

  2. #2
    Join Date
    Dec 2007
    Location
    Cedar Grove, Wi-Sheboygan
    Posts
    1,582
    Wasn't there a post not too long ago about this issue with another poster who had similar problems with the fan running and blowing the same as was explained here in this post. If I remember correctly the fan wiring was backwards or wiried in reverse polarity causing the fan to blow dow and out the side of the OD unit ? Something to check.

  3. #3
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    401
    Found the same thing last week. 3ph. motor. switched 2 legs and good to go.

  4. #4
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    I have found it a number of times, twice the motor wouldn't reverse and had to be replaced... both times a trip saver motor.
    ___________________________________________


  5. #5
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,876
    I have seen it a few times too...resi and commercial both.

    Nothing better than when I would get one on a Voyager.....one fan pulling air in and the other pushing it out....not a damned bit of air across the coils! LOL

    How does someone use a "trip saver" and then not check the rotation after they put it in?? Job security....
    I need a new signature.....

  6. #6
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Well thats what I said too.... but in both cases, it would'nt reverse
    ___________________________________________


  7. #7
    Join Date
    Dec 2004
    Posts
    201
    Capacitor ?

  8. #8
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,876
    Quote Originally Posted by filterchanger View Post
    Capacitor ?
    I have seen those cause this as well
    I need a new signature.....

  9. #9
    Join Date
    Aug 2007
    Location
    Spartanburg, S.C.
    Posts
    58
    All of the responses will be very helpful. I have been going through different things in my mind. I will keep yall posted.