    10 ton unit with a long line set

    I installed a 10 Ton unit and the closest place available was 200' away with a vertical raise of 30' and 170' horizontal, I over sized the suction line from 1 1/2" to 1 5/8" and liquid line from 1/2" to 5/8". can someone tell me if I have to install anything on the line to make it work since I have no other closer option and I keep burning compressors because of low suction and compressor running dry of oil????

    Please post any ideas or suggestions.
    Last edited by abcool; 06-02-2008 at 11:03 PM.

  2. #2
    Join Date
    Apr 2006
    Location
    Motel 6.5
    Posts
    148
    Check the IOM for piping details. That is ALOT of pipe and much juice to migrate. I would be concerned about washout and oil loss.

  3. #3
    Join Date
    Nov 2007
    Location
    I am unsure myself
    Posts
    1,117
    are there any traps?

  4. #4
    Join Date
    Jun 2008
    Posts
    12
    inverted trap at the condensor

  5. #5
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    1,682
    There should be a p-trap in the suction line every 20 feet of rise in a system with normal pipe lengths and sizes. With a bigger suction you'll have less velocity to bring the oil home, and may need to cut down on the rise between traps.

    I'd be for a careful look-over of the whole system and find the places where the oil is sitting. Take a bucket if you cut into anything.
    God Bless the USA

  6. #6
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,385
    double check that trap thing, always check with the manuf. A lot of them discourage them now-a-days and just make the suction line a bit smaller (to increase velocity)
    "If you call that hard work, a koala’s life would look heroic."

    VETO PRO PAC, The Official Tool Bag of HVAC-Talk.com

    Testo... you guys rule!

  7. #7
    Join Date
    Jun 2008
    Posts
    10
    I have 2 reverse p-traps one at air handler and 1 at condenser but not on the rise. I also installed a liquid line solenoid valve before the air handler.

  8. #8
    Join Date
    May 2008
    Location
    Cebu City, Philippines
    Posts
    38
    http://www.hvactc.com/ref_basics/800...eat_pumps1.htm

    see accumulator discussion at this site. Shows you the trap with orifice as a venturi

    regards,
    MorZy

  9. #9
    Join Date
    Jun 2008
    Posts
    10
    the rise is 10' in basement and then horizontal for 70' another 17' rise and 90' to 100' horizontal in the roof where the cond unit is

  10. #10

    What kind of failures are you experiencing

    Have you tried to fix any open issues, what are symptoms causing unit to fail

  11. #11
    Join Date
    Jun 2008
    Posts
    10
    Quote Originally Posted by Randy S. View Post
    There should be a p-trap in the suction line every 20 feet of rise in a system with normal pipe lengths and sizes. With a bigger suction you'll have less velocity to bring the oil home, and may need to cut down on the rise between traps.

    I'd be for a careful look-over of the whole system and find the places where the oil is sitting. Take a bucket if you cut into anything.
    I have 2 reverse p-traps one at air handler and 1 at condenser but not on the rise. I also installed a liquid line solenoid valve before the air handler. The rise is 10' in basement and then horizontal for 70' another 17' rise and 90' to 100' horizontal in the roof where the cond unit is

  12. #12
    Join Date
    May 2008
    Location
    Cebu City, Philippines
    Posts
    38
    hard to figure it out. you mean your condenser is above level of the evaporator?

    Usual life of your compressor? Reciprocating? or Scroll?

  13. #13
    Join Date
    Jun 2008
    Posts
    10
    simptoms are low pressure on suction line, almost 60 lbs of refrigerant and still cycling off for low pressure, the TXV bulb is placed on suction line but it freezes as soon as I start the unit