    geothermal standing column well capacity

    So geo designers, what tonnage can this well support? I'm looking for 7.5t of HEATING if I can get it. Cooling is much less critical we are on the coast and rarely use the ac.
    Well is not used for domestic water, but is used for irrigation in the summer.
    good disposal available for bleed water.
    The standing column well capacity numbers I have seen run from 46ft/ton to 100ft/ton thats quite a range.

    boston area 52f water temp
    bedrock well
    510' hole
    6" diameter
    20.6'static
    drawdown test pumped at 7gpm for 4 hours results below:

    time (min) dist to water ft
    0 20.6
    15 35.8
    30 41.2
    45 55
    60 61
    75 65
    90 68
    105 74
    120 78
    135 80
    150 84
    165 86
    180 88
    195 90
    210 92.5
    225 94.3
    240 97
    255 99

    obviously if the hole can support my tonnage i would not redrill it or frac it.

    Thanks
    D
    Quick reply to this message Reply  

  2. #2
    Join Date
    Feb 2007
    Location
    out in the country
    Posts
    637
    Post Likes
    Just a couple of thoughts here, 7.5 ton takes a lot of water per minute. If you draw down the water level in the well you will need to over come the lift (feet of head) meaning it will require a sizable pump. Properly sized your unit will probably run constantly in the coldest part of the year = draw down of water level. Also you mentioned you have good disposal area for your water, hopefully this is a dry lake area cause it's gonna make a big puddle that may freeze when the od temp is low enough. BTW I don't design geo loops open or closed. And I'm not trying to talk you out of a geo unit.

    Looks like you may already have considered some things, and done some homework ,just wanted to share some thoughts,

    iso
    I never let schooling interfere with my education... Mark Twain
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jan 2002
    Location
    Ft.Worth,Tx
    Posts
    4,809
    Post Likes

    Geo Thermal Wells

    Most of our wells , vertical are 220-300' per (1) ton of a/c spaced min. 10' apart and ranges are different on lift by pipe size/pump gpm.

    Might want to call Tom Willis at:
    http://www.earthenergytech-supply.com/

    He has always help us in our wells and been drilling geo's for years.
    'Life begins with the journey each day'
    Quick reply to this message Reply  

  4. #4
    Join Date
    Feb 2007
    Location
    out in the country
    Posts
    637
    Post Likes
    Normally in our area closed loops are around 200' per ton, But my understanding is the OP is planning on a pump and dump geo. Water quality would be a big issue, most pump and dump systems around here have problems with strainers, HX, and flow valves failing because of clogging. Also the cost of operating the pump will offset some of the savings. And a dry spell may affect the water levels of the well.
    I never let schooling interfere with my education... Mark Twain
    Quick reply to this message Reply  

  5. #5
    Join Date
    Apr 2005
    Location
    NE PA
    Posts
    698
    Post Likes
    Figure you should have 20-25 GPM for that sized unit. At 200' lift head that is close to 3 HP. That will be a lot of power just for the water, assuming the well can support that type of flow.

    paul
    Quick reply to this message Reply  

  6. #6
    Join Date
    Nov 2007
    Posts
    87
    Post Likes
    Without going into all the issues regarding open loop systems, at 7.5-tons, you will need to pump at least 18gpm, minimum. However – consult the installation manual specifications for the specific WSHP you intend to install, that will be the final authority on your requirement.

    Consult a professional well driller or knowledgeable geothermal installer/designer to verify the capacity of your well.

    SR
    Quick reply to this message Reply  

  7. #7
    Join Date
    Nov 2007
    Posts
    87
    Post Likes
    I wish to correct my last post. 7.5-T = 24USGPM min. Consult manual & professionals.

    IMO

    SR
    Quick reply to this message Reply  

  8. #8
    Join Date
    Apr 2008
    Posts
    23
    Post Likes
    Thread Starter
    consult professionals:

    thats why i am here. nobody here seems to know much about scw heat exchange capacity. just looking to check my pro's #'s before dropping big bucks on a geo.
    wall of shame is not a fun place to hang out.


    D
    Quick reply to this message Reply  

  9. #9
    Join Date
    Dec 2007
    Location
    oregon
    Posts
    885
    Post Likes
    is this a commercial system or two units on a residential building?
    Genius = The guy who can do anything...except make a living!
    Quick reply to this message Reply  

  10. #10
    Join Date
    Apr 2008
    Posts
    23
    Post Likes
    Thread Starter
    its 2 in a residence.

    D
    Quick reply to this message Reply  

  11. #11
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    WildWillT

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.

    Your post has been deleted.


    Quick reply to this message Reply  

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Closed old thread


    Quick reply to this message Reply  

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •