Results 1 to 9 of 9
    Dubai
    Question 30 gx carrie chiller tripping
    hi
    my 30 gx carrier screw chiller tripping on alrarm code 101.this code not in service manual.if i expan the the display shows motor tmperature is high.before tripping compressor temp:is 116c.for your info othor readings are
    suction pressure 40
    saturated discharge temp:50c
    saturate suction temp: 4.7c
    discharge gas temp: 82.4c
    discharge superheat 32.3c
    motor temp: 113c
    can anybody solve this problem?
    Wichita Ks
    is your motor cooling circuit working? if your low on freon you will over heat. the motor cooling liquid line needs to be full of liquid at all times. How far is your expansion valve open? it is probally 100% which would be another clue of low on charge.
    Aug 2000
    Under my tree
    Thats 235F which is way to high. Whats the status of your motor cooling valve? What is the the TXV position? Possibly low on gas like FR stated or motor cooling problem.
    To much work with too little time!!!!
    Dubai
    thanks to absrbrtek and freonrick.motorcooling solinoid is working.this prodialoge display(in output mode)doesnt show the EXV position.compressor tripping after compressor reach 100% full load.can possible to fixe a extra cooling solinoid?if possible,could you tell me the orifice size and details?
    Cartersville Ga
    have you checked the motor cooling filter /drier? is the motor reaching trip point?
    East of big city prices.
    Is your suction pressure in psi kpa? What part of the world are you in haven`t seen too many GX`s here with the touch pilot around here? What is the full model number on this thing?
    uk
    Quote Originally Posted by moideen View Post
    hi
    suction pressure 40
    motor temp: 113c
    Hi Moideen
    You need to give more information.
    1 What is your chilled water in and out.
    2 Condenser air on and off
    3 Liquid line temperature
    4 What is the subcool.
    5 What version of Pro Dialog do you have is the display black or cream coloured.
    it sounds as if you have a version 2 can you give me the date of manufacture.
    6 Is the discharge superheat taken from the display or are have you measured this.
    32.3C is high the control point is 11.1C
    7 You are sure you can't read the EXV position from the display.
    8 Is the sightglass full or flashing when compressor reaches 100 % full load
    9 Suction and Discharge pressures What is your display reading psi or kpa
    The motor temp has reached its trip point if it has gone over 110C there is a 2nd sensor connection in the compressor terminal box you will see 3 spade terminals 1 of which is common. You can check your current sensor againest the other one. Be sure to switch off mains power before checking this.
    Wichita Ks
    Quote Originally Posted by Sucurro View Post
    30 G X Chiller tripping on low discharge superheat.
    you need to start a new thread
    It sounds like you need to raise your discharge superheat.