    btus-input vs output?

    I just got my last quote from a Lennox dealer. As some of you know, the recommended size for a new furnace has ben all over the place for my home. This guy is quoting for a 90,000 btu, which, by what all of you have been saying is way oversized. When I questioned him about it, I learned this tidbit of info - true or not?:

    a 90,000 btu 80% furnace has an input of 90,000, but only puts out 63,000 btus. A 70,000 btu would put out 54,000, which maybe insufficient on coldest days. Furnace quoted is the G50UH36B-090.

    He is also recommending a 3 ton ac, where everyone else has said 2.5. An XC13, which would be "increased by the coil to 14 seers".

    No, he did not do a load calc. Said it's not the only thing to go by, judged windows, ducts, insulation, room sizes, etc, etc.

    I was seriously considering his proposal, since the Rudd dealer hasn't called me back from last Friday, and the equipment specified (except for size) and price seem okay. But if I insisted on him recalculating my needs, and sizing properly, could I trust his install? Or should I just forget this one completely?

  2. #2
    Join Date
    Apr 2001
    Location
    Camel City, NC
    Posts
    6,234
    Post Likes

    Gas & Oil

    Gas furnaces are expressed in input. Oil is expressed in output.
    90K 80% gas should be 90,000 x .80 = 72,000. 90k oil is 90k output. There are other things that can effect rated output. Thats the simple answer.
    Be safe not fast. body parts don't grow back

  3. #3
    Join Date
    May 2008
    Posts
    22
    Post Likes
    Thread Starter
    Thank you for clearing that point up for me. Then he is correct in his statement, but still off on sizing .

  4. #4
    Join Date
    Feb 2007
    Posts
    1,002
    Post Likes
    Quote Originally Posted by MGM2 View Post
    Thank you for clearing that point up for me. Then he is correct in his statement, but still off on sizing .
    ???

  5. #5
    Join Date
    May 2008
    Posts
    22
    Post Likes
    Thread Starter
    Quote Originally Posted by ampulman View Post
    ???
    Several other installers on here said there's no way my 1500 sq ft house would need a furnace that big. My estimates have been all over the place. It seems they're just guestimating, not doing load calcs.

  6. #6
    Join Date
    Apr 2001
    Location
    Camel City, NC
    Posts
    6,234
    Post Likes
    I wasn't in on your origional post about the sizing, so I recommend this http://hvaccomputer.com/talkref.asp If you take the time to do it correctly there won't be any question about sizing.
    Be safe not fast. body parts don't grow back

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    He doesn't want to, or doesn't know how to do a load calc. JMO

    As said earlier, a 90,000BTU input 80% is 72,000 BTU output.
    An 80,000 BTU input 90% would be 72,000 BTU output.

    You might want to use teh hvac calc program and do your own, and decide from there who you want to use, if you can't find a comtractor to do a load calc for you.

  8. #8
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    Quote Originally Posted by MGM2 View Post
    Furnace quoted is the G50UH36B-090.

    just to throw another wrench into all of your figuring......... actual input of that furnace is only 88,000 btu's, 070 furnace wouldbe 66,000 btu input.
    all Lennox furnaces are 22,000 btu's per burner.

    if load calc is between the 2 sizes maybe a G60uh or G60uhv 2 stage furnace would be a better fit........

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    That would still give outputs of, 70,400 for the 88,000 at 80% and 52,800 for the 66 at 80%.

    And a house that may only need 36 to 45,000.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •