    carrier economizer

    this is a smaller unit with just the standard economizer board. this building has 2 rooftiops. they are set up for differential enthalpy control set on d. the problem was they were calling for free cooling with 80 deg temps. i replaced the od air sensors to foolow up from another techs service call. i replaced them. with set on d mechanical cooling came on damper closed. switched to a and economizer came on mechanical cooling off. now today same thing no ac both calling for free cooling with 80 deg temps. everything wired right. control board is a hhg3aw001 od sensor hh57ac074 any ideas

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,550
    Is it the honeywell board and where are you located ,like outside airtemp and humidity? Maybe a full model # too.

  3. #3
    Join Date
    Nov 2004
    Posts
    209
    When you say the standard econo board, most of us would think honeywell W7459. but the #'s you gave look like the Novar EconoMi$er+ package.did you verify 18 to 24VDC from contoller? and did you you measure the 4 to 20mA signal in the enthalphy circuit compared to ambiet conditions? before you replaced sensors. Do you have any more info? we want to help

  4. #4
    Join Date
    Apr 2007
    Location
    In my service van checking my lotto ticket
    Posts
    641

    Same thing...

    I heard another tech at the shop had almost the same thing going on with a couple of carriers but the units were calling for 100 OA damper position and the compressors were coming on! I would like to hear if anyone else has the same thing going on.

    He said he just ended up pulling the 24 volts from the OA controller. He also stated that he checked for the right connections and wiring of the differential ethalpy and all was OK on that end of it.


    things that make you go HHHHHHUUUUMMMMM....
    "If you can't explain it simply, you don't understand it well enough”
    Albert Einstein

    "Don't you just love when the flames burn off the wiring schematic?" hvacvegas-HTALK member

    On Monday, not even the chickens lay eggs...

  5. #5
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,474
    Quote Originally Posted by hvac17011 View Post
    this is a smaller unit with just the standard economizer board. this building has 2 rooftiops. they are set up for differential enthalpy control set on d. the problem was they were calling for free cooling with 80 deg temps. i replaced the od air sensors to foolow up from another techs service call. i replaced them. with set on d mechanical cooling came on damper closed. switched to a and economizer came on mechanical cooling off. now today same thing no ac both calling for free cooling with 80 deg temps. everything wired right. control board is a hhg3aw001 od sensor hh57ac074 any ideas
    If you are using differential enthalpy, you need to check the return air enthalpy sensor, if that is faulty then the control could be reading higher enthalpy in the return air than the outside air.

    Kevin
    "Profit is not the legitimate purpose of business. The legitimate purpose of business is to provide a product or service that people need and do it so well that it's profitable."

    James Rouse

  6. #6
    Join Date
    Jan 2001
    Posts
    710
    The model of the unit is a 48tme009601hq. the numbers in previous were carriers numbers. i tried removing return sensor which should make it just looking at outside air but it did the same thing. I have 2 units sitting side by side doing the same thing the one unit has 2 stages of cooling and the compressor was running. the manual says doing a checkout with several resistors and a 9v battery but i didnt have resistors.

  7. #7
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    1,952
    Quote Originally Posted by xarralu View Post
    I heard another tech at the shop had almost the same thing going on with a couple of carriers but the units were calling for 100 OA damper position and the compressors were coming on! I would like to hear if anyone else has the same thing going on.

    He said he just ended up pulling the 24 volts from the OA controller. He also stated that he checked for the right connections and wiring of the differential ethalpy and all was OK on that end of it.


    things that make you go HHHHHHUUUUMMMMM....

    a call from y2 will bring the mechanical cooling online even with free cooling available.

  8. #8
    Join Date
    Apr 2007
    Location
    In my service van checking my lotto ticket
    Posts
    641

    Answers that question

    Huh, did not know that. Ill pass it on...
    "If you can't explain it simply, you don't understand it well enough”
    Albert Einstein

    "Don't you just love when the flames burn off the wiring schematic?" hvacvegas-HTALK member

    On Monday, not even the chickens lay eggs...

  9. #9
    Quote Originally Posted by y7turbo View Post
    a call from y2 will bring the mechanical cooling online even with free cooling available.
    but shouldnt the oa damper shut to minimum at that point?

  10. #10
    Join Date
    Nov 2004
    Posts
    209
    Quote Originally Posted by brandewski View Post
    but shouldnt the oa damper shut to minimum at that point?
    not with a 2 stage t-stat and the OA is ok for free cooling,the economizer is first stage and the compressor is second stage creating an integrated economizer.
    AIRFLOW IS CRITICAL

  11. #11
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    1,952
    Quote Originally Posted by brandewski View Post
    but shouldnt the oa damper shut to minimum at that point?
    if were talking about your normal honeywell 7459 , he dampers should modulate to keep a discharge temp of 50-55. or is it 55-60? i have to look in my book. too many damn things to remember! lol

  12. #12
    Join Date
    Mar 2003
    Posts
    7,253
    Differential enthalpy set up look at the total heat content of each airstream. If the oa was less than the return, it could do what you suggest. Are you using the right sensors? the carriers usually ship with a single sensor which is temp only, and for diff enthalpy you need to replace both. When you removed the return sensor, did you install the resistor across the terminals?? confusing the controller will only confuse you more.

  13. #13
    Join Date
    May 2008
    Location
    Jax Fl.
    Posts
    1,942
    According to EPIC, you have a digit off in your part number for the econo controller. I think it should be HH63AW001. The sensor number is correct.