    semi hermetic compressor pins broke

    Have a carlye 06E semi hermetic which has 2 pins holding the reeds in place and the pins broke off flush with the compressor. Tryed to drill them out with a cobalt drill bit but getting no where fast and just breaking the little bits. any suggestions.

  2. #2
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    i would of tried a strong magnet

    since you already tried to drill it, it may be to late!



    .
    Last edited by Airmechanical; 05-25-2008 at 11:36 AM.

  3. #3
    Join Date
    May 2008
    Location
    Southern California
    Posts
    55
    I'm curious to hear if anyone has a way to get them out.
    I have tried everything I could think of and it always comes down to replacing the compressor. I don't feel too bad about that as the one I had last month was installed in 1982.
    Also, with a bad valve after awhile the heat starts tearing up the guts. I've had enough of them fail in the months right after putting a valve plate on that I don't even like to that unless it is a fresh compressor.
    Have fun, be safe,
    Mike

  4. #4
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,415
    How big are the pins? Something like 1/4" if I recall in my fuzzy memory.

    Could use a dremel with a diamond bit to bore it out. Or, if possible, bore a small hole in it, thread a zerk in it and pump grease in it. If the hole (in the compressor) is sealed, when you pump the grease in it'll push the pin out.

    In general I'd say that's way too much work for an old compressor... just replace it. It's just money
    "If you call that hard work, a koala’s life would look heroic."

  5. #5
    Join Date
    Dec 2007
    Location
    Frognot TX
    Posts
    836
    I can tell you how to stop it from happening, loosen, do not remove the head bolts, and hit the head dead center with a hammer, and it will pop the head and valve plate loose.

    To get it out try a strong magnet, if you've drilled on it they may not come out.


    Yeah I've screwed one or two up before

  6. #6
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    ...and I thought dropping them in the compressor was bad

  7. #7
    Join Date
    May 2008
    Location
    Southern California
    Posts
    55
    1/4" sounds like the pins on a 5h.
    The 06s are less than 1/8 and the valve just cuts through them after many years.
    Mike

  8. #8
    Join Date
    Dec 2007
    Location
    Frognot TX
    Posts
    836
    Not if the valves are put in right, but if they are worn out from the valves, you need a new comp any way

  9. #9
    Join Date
    Jan 2002
    Posts
    44

    broken pins

    had same problem, drilled small angled hole toward broken pin, took a while and several bits, used dental pick to remove broken pin, epoxied in new pin.

  10. #10
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    5,535
    Quote Originally Posted by ceg22 View Post
    had same problem, drilled small angled hole toward broken pin, took a while and several bits, used dental pick to remove broken pin, epoxied in new pin.

    I've also heard that. Center punch near the pin and drill at an angle with a 1/16" bit or a little larger.
    It's usually the valve plate locator pins that break when the tech smacks the head on the side.
    Tracers work both ways.

  11. #11
    Join Date
    May 2001
    Location
    Houston
    Posts
    29
    I did repairs on this problem a couple of times.
    You have to drill a small hole next to the broken pin just large enough to pick the pin out from the bottom. It may have to be at a slight angle. You cannot drill throught the pin. Pry the broken pin out.
    Now drill out the hole with a 1/4 or 5/16 drill usining the pin hole as center. Dont go too deep.
    Get a 1/4 or 5/16 brass rod that is a little higher than the face of compressor valve machining, maybe a 1/32 inch. Hit the rod with a hammer into the hole. It will expand in the hole and set itself. You may have to file a little off to make it flush.
    Now you need an old valve plate the same size to use as a template for the new pin hole to be drilled into the new brass plug. You have to drill the pin holes throught the old valve plate. Use the exact size drill as the hole for the pin in the plate. Set the old plate on the good pins and drill out the new hole. Not too deep.

    It is quite a bit of work but I have never had one fail.

    Glen

  12. #12
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    5,535
    As often as this has happened I wonder why Carrier doesn't do a Copeland or at least something else. Even a label.
    Tracers work both ways.

  13. #13
    Join Date
    May 2008
    Location
    Jax Fl.
    Posts
    1,943
    When they sheared off in the body, I just cut the end off of a new dowel pin and inserted it [partially sticking out] of the valve plate. The broken end [in the body] and the cut end butted on top on each other. The valve has to be held in position while you are placing it on the body [kind of a pain].

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event