    Majestic A132 - Shutting Down When Valve Turned to " ON "

    As the title states I have looked at a fireplace, the pilot stays lit when on pilot, as soon as you turn valve to " ON " it completely shuts down.

    The thermopile is generating 525MV with the wall switch off, about 300 with the switch on.

    Could this be a vent switch (i'm think the vent switch would prevent the pilot form coming on but not 100% sure ?)

    The unit has been idle for a couple of years. I have checked the main orifice and burner tube and they are free of debris.

    I'm leaning towards faulty valve but looking for opinions as I am typically a furnace guy, trying to help a buddy out.

  2. #2
    Join Date
    Nov 2009
    Location
    Simcoe, ON Canada
    Posts
    46
    Does it have a Honeywell Valve? They were wellknown for this problem. If so your only choice is to change out the valve. Contact Vermont Castings group for the kit number.

  3. #3
    Join Date
    Nov 2010
    Location
    Ontario, Canada
    Posts
    68
    Quote Originally Posted by robatnorfolk View Post
    Does it have a Honeywell Valve? They were wellknown for this problem. If so your only choice is to change out the valve. Contact Vermont Castings group for the kit number.
    Thank you for the response it is very much appreciated. Not sure which valve it has, didn't reaize this model came equipped with different valves until doing some research. I will be checking which one it is.

    If the vent switch is tripped the pilot will not light, correct?