  1. #14
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,189
    You have a variable drive compressor. Different beast.
    Perhaps you should have read the instructions before calling.

  2. #15
    Join Date
    Apr 2008
    Location
    Alberta Canada
    Posts
    2,246

    you can turn down humidity

    Just have to go into advanced options and put in manual settings instead of auto tracking out door settings. When you have it in auto setting you can only adjust range which is a small margin, that is where you see bars. You can actually set as low as you want.
    Do it right the first time.

  3. #16
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,189
    Quote Originally Posted by 21degrees View Post
    Just have to go into advanced options and put in manual settings instead of auto tracking out door settings. When you have it in auto setting you can only adjust range which is a small margin, that is where you see bars. You can actually set as low as you want.
    Auto Tracking with ODT is for heating humidification.
    Perhaps you should have read the instructions before calling.

  4. #17
    Join Date
    May 2007
    Location
    Naples, Fl
    Posts
    889
    Just say no to droop. A dehumidifier does not sweaty ducts make.

  5. #18
    Join Date
    Aug 2007
    Posts
    273
    I noticed the same issue with my Infinity system which has a variable speed motor. What ever you try, it cannot be set lower than 46% in any configuration including non auto. I recently purchased a stand alone dehumidifer to help control humidity in my basement in the early summer months before the cooling season starts in earnest.

  6. #19
    Join Date
    May 2008
    Location
    Houston
    Posts
    7
    PRODUCT DATA INFORMATION
    Compatible Communicating Products
    Air Conditioning units -- 24AN1, 24ANA7, 24APA5, 24APA3
    Heat Pumps -- 25HNA6, 25HNA9, 25HPA3, 25HPA4,
    25HPA5
    Gas Furnace -- 58MVB, 58MVC, 58CVA, 58UVB
    Fan Coils -- FE
    Small Packaged Products -- 50XL/XT, 50DU/DT, 50CE/CR,
    48XL/XT, 48DU/DT, 48CE
    Physical Characteristics
    Dimensions: See drawing
    Appearance: Plastic, white color, textured
    Electrical Characteristics/Communication
    Input Volts/Amps 24VAC
    Each device in the Infinity System has a four--pin connector
    labeled ABCD. It is recommended that the following color
    code be used when wiring each device:
    A — Green = Data A
    B — Yellow = Data B
    C — White = 24VAC (Com)
    D — Red = 24VAC (Hot)
    Environmental Requirements:
    Operating Temperature/Relative Humidity:
    User interface and all sensors: 32_F to 104_F / 0_C to 40_C,
    95% rh non--condensing
    Storage Temperature/Relative Humidity:
    User interface: -- 40_F to 134_F / --40_C to 56.7_C, 95% rh
    non--condensing
    Feature Specifications:
    Temperature set point range: 40_F to 90_F / 4.4_C to 32.2_C
    Separate heat and cool setpoints
    Programming days: 7 day
    Programming periods:
    2--Day, Sleep
    4--Wake, Day, Eve, Sleep
    Non--Programmable
    Auto changeover (may be disabled)
    Programmable fan (installer selectable)
    Humidity Sensor Offsets
    Auto Changeover Timer (installer adjustable)
    Smart Recovery (in heating and cooling)
    Hold function
    Copy functions: Copy period, day and zone
    Permanent memory
    Humidity display and control
    Temperature sensor offsets (indoor and outdoor)
    TrueSenset Dirty Filter Detection

    As I look threw the product data I dont see any information, ill keep an eye open to see if i can find any info.

  7. #20
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,189
    When you take this system below 46% rh and 70F, you are entering low ambient operations.

    Your system is not designed to operate in this manner.

    Buy a dehumidifier. Seal your home.
    Perhaps you should have read the instructions before calling.

  8. #21
    Join Date
    Apr 2008
    Location
    Orange County, CA
    Posts
    42
    acmanhoney, When I set it to 46% and the dehumidify is set on, no it does not cool beyond the set temp. It should, but it turns off at the set temp. I wonder if it has a differential humidity difference that says it is close enough? It was just installed and the Puron pressure was calibrated. How can I tell if I have a leak?

    jrbenny, The system temp is set for 78F, not 70 nor has been 70 when it limited me to 46%. Are you saying it limits me to 46% in case it hits 70? Then why not limit me to 50% in case it might drop to 65F?

    Can a Carrier Infinity knowledgeable person confirm that it truly can't be set below 46%? Or can I talk to someone at Carrier? And I apologize if someone already has given me a clear answer has it is hard to tell what knowledge level some of the statements made on here are based on. This is not really a HVAC question but a Infinity question. So no disrespect meant again.

    Thanks again,

    Keith

  9. #22
    Join Date
    May 2008
    Location
    Houston
    Posts
    7
    Quote Originally Posted by OldSoCalCondo View Post
    acmanhoney, When I set it to 46% and the dehumidify is set on, no it does not cool beyond the set temp. It should, but it turns off at the set temp. I wonder if it has a differential humidity difference that says it is close enough? It was just installed and the Puron pressure was calibrated. How can I tell if I have a leak?

    jrbenny, The system temp is set for 78F, not 70 nor has been 70 when it limited me to 46%. Are you saying it limits me to 46% in case it hits 70? Then why not limit me to 50% in case it might drop to 65F?

    Can a Carrier Infinity knowledgeable person confirm that it truly can't be set below 46%? Or can I talk to someone at Carrier? And I apologize if someone already has given me a clear answer has it is hard to tell what knowledge level some of the statements made on here are based on. This is not really a HVAC question but a Infinity question. So no disrespect meant again.

    Thanks again,

    Keith

    I can get you just about any information on the infinity systems but allot of times the product data is...somewhat Baud , I would have to speak to technical support and see what they say...may take me a day or so to get a straight answer but ill see what I can do.

    *Edit*
    Do you happen to have the full model number of your controler. Carrier has came out with a couple different models over the past 3 or so years

  10. #23
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,368
    Jrbenny use to be a Carrier rep.
    I would think he is giving you the correct info.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #24
    Join Date
    Apr 2008
    Location
    Orange County, CA
    Posts
    42
    Oh, and Carriers marketing says things like:

    "Superior humidity control" - For Infinity AC.
    "Infinity™ Control—you have precise control over temperature, humidity, ..." - For the T-stat.

    "IdealHumidity
    Keeping your home comfortable at any temperature
    IdealHumidity

    Innovative Carrier IdealHumidity™ systems constantly control both temperature and humidity, day and night, in any season. With an IdealHumidity system, you can monitor and adjust your home's humidity level even when your home comfort system isn't actively heating or cooling. Maintaining the proper balance of moisture in your home keeps you more comfortable at higher temperatures in the summer and lower temperatures in the winter.

    In the summer, Carrier variable-speed blower systems work in concert with Carrier's highly refined Thermidistat™ Control to remove up to 30 times more moisture than a standard system, keeping you cool and more comfortable. Plus, it can also save you up to 21% in cooling costs."

    IdealHumidity doesn't say it will add humidity it just says it will remove up to 30 times more then a standard system. Well I have that variable speed blower.

    This all points a pretty strong picture that it will do a superior job of controlling humidity. I don't think any one would think the lowest setting of 46% is superior.

  12. #25
    Join Date
    Apr 2008
    Location
    Orange County, CA
    Posts
    42
    Thanks jrbenny, let me know what you think and how sure you are. This is an important issue for me so I do appreciate the help. Thanks beenthere for letting me know jrbenny's background, that helps.

    Hartmizle, thanks, I would appreciate that a lot. Below are all my system details.

    Carrier Condenser - 24ANA724A003
    Carrier Furnace - 58CVX070112
    Carrier Coil - CNPVP2414ACA
    Infinity Control - SYSTXCCUID01-B
    Software Version - CESR131339-13


    Thanks again.

  13. #26
    Join Date
    May 2008
    Location
    Houston
    Posts
    7
    Waiting for a response back from Tech Support

    If you want to change the way cooling dehumidification is
    controlled, scroll to DEHUMIDIFY. You will have two options.
    OFF – The system will not activate the cooling equipment to
    dehumidify if the cooling temperature has been satisfied.
    ON – The system dehumidifies by activating the cooling
    equipment – even after the cooling temperature has been
    satisfied. The system will not cool to dehumidify below 70° F
    in order to protect equipment.
    Your air conditioning system will provide excellent
    humidification control with DEHUMIDIFY set to either ON or OFF.
    However, you will receive better humidification control with
    the ON setting.

    You may already have this information but its the only thing I found worth posting for the time being.

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event