    Quote Originally Posted by menaphnx View Post
    what cause a sweating suction line in a split system?

    my suction pressure was 68 psi and my high was 224 psi .

    Can it be undercharged or overcharged?

    dirty indoor coil?


    pls help

    thanks
    In my opinion you've left out quite a bit of important information. Whats you indoor metering device (this determines the method for verifying correct refrigerant charge)? Once you've determined method for checking charge, what is the required superheat or subcooling. What are you indoor and outdoor temps (wetbulb and drybulb)? The past few days where I am its been very cool for august (79 degrees high temp) and very dry. I've had 53 degree suction lines that aren't sweating simply because with the low temp and humidity they suction lines are above the dew point.

  2. #15
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,905
    get out thecold beer can if they are the same temp your good to go the indoor temp dont matter