Results 1 to 13 of 15
    Phoenix AZ
    Confused sweating suction line
    what cause a sweating suction line in a split system?
    my suction pressure was 68 psi and my high was 224 psi .
    Can it be undercharged or overcharged?
    dirty indoor coil?
    pls help
    thanks
    Most of the time it is below the dewpoint and will sweat. That's why the insulation is on it.
    May 2008
    newnan,ga
    Is the suction line insulated?
    What baldie said.
    Its normal.
    Remove those guages, and step away from the unit.
    Checking the charge is not a DIY thing.
    May 2008
    The People's Republic of Massachusetts
    A suction line will sweat is can even have ice and be OK. As long as the ice goes no farther than the end bell on the compressor it is nothing to really worry about. A little frost on the end bell is just good subcooling for the compressor.
    Phoenix AZ
    thanks all!
    Talking
    you're unit is working like its supposed to put those gauges on ebay!
  8. Likes RichO liked this post
  9. #8
    Dec 2006
    Middle Tennessee
    Quote Originally Posted by maints View Post
    A suction line will sweat it can even have ice and be OK. As long as the ice goes no farther than the end bell on the compressor it is nothing to really worry about. A little frost on the end bell is just good subcooling for the compressor.
    must be a maintanance guy thing
  10. #9
    SW Wisconsin
    If an uninsulated suction line is below the Outdoor Ambient Temp (OAT) dew point it will condense moisture. Of course, the OAT dew point can vary a great deal; just ignore the sweating issue. (Where is the insulation?)
    Forget about a sweating suction line, it is NOT an indication of an incorrect charged system.
    Get the airflow right & the Superheat & Subcooling within specifications.
    AOP Forum Rules:
    Rules for Posting
    Rules For Equipment Owners
    Equipment Owners Find a Contractor HERE!
    Free online whole house load calculator & Sizing: http://www.loadcalc.net/ Anyone can use it...!
    udarrell
  11. #10
    East of big city prices.
    If suction didn`t sweat you wouldn`t need a drain pan.
  12. #11
    Phoenix AZ
    Quote Originally Posted by Airmechanical View Post
    you must be a comedian on the weekend
  13. #12
    He probably found the ice on the compressor comment funny for an A/C compressor.
  14. #13
    May 2008
    You can have frost on the endbell of the compressor it does no damage. And I'm talking refrigeration not AC. You'll have an oil failure before your compressor dies from a slug of liquid. Again refrig not AC