    Hi I’m new in the business and trying to learn as much as I can and looking to get some help from you guys. I’m having a problem with my own A/C unit and can’t figure out what’s going on with it. Here is the situation:
    I’m getting a very low Delta T, around 6 degrees difference… 73 degree return air and 67 on supply. I put my gauges on and got 20 psig on the low side and 157 on the high side. The indoor temp was 75. The outdoor temp was about 80 to 85. The suction line temp at the condenser was 77. I checked the air filter, evaporator coil and condenser coil to make sure there was no blockage. I then felt the evaporator coil and found that it was cold only about 40%. It has a fixed metering device/cap tube. Being the rookie that I am, I decided that the evaporator was starved and to add some refrigerant (yes I do have my CFC) about 2 pounds. I fully expected the gauge pressures to rise and the suction line temperate to drop and I was ultimately hoping to get a 10 degree superheat based on my A/C charging calculator.
    After adding refrigerant the low side gauge rose to around 38 psig and the suction line temperature lowered only to 70 degrees. In my mind this equates to about 15 degrees saturation temperate and about 55 degree superheat. After realizing that adding refrigerant was not solving the problem, I put my tools away for the day and decided to think on it. Today I hooked up the gauges again and found that I’ve got 100 psig low side and 175 psig high side. The suction line temp was 70. I’m pretty confused about the change in pressure. I checked the evaporator coil and it’s still running only about 40% cool.
    I appreciate any feedback.
    Thanks,
    Jul 2001
    maryland
    I think you should put some more in it.
    ID WB temp, OD DB temp, SH, and SC???
    Sep 2006
    Tampa Fl
    "I’m new the business"
    Sounds like India to me!!!
    Florida
    Sounds like DIY to me, or someone that can't read the rules.
    Fort Worth, TX
    If you stop and think about "sequence of events", you can often answer your own questions (not always, but mostly). Review what you first found, what you did that you thought would change things, and then the end result.
    Your first assumption after your gauge and superheat readings was that the system was low on refrigerant. Adding refrigerant did not restore proper performance of the system. When you returned a day later, your readings were worse. What happened?
    First of all, unless you merely forgot to include such in your post, you did not measure subcooling, nor disclose what amperage the compressor was pulling under all three observation sets (when you first found it, after adding refrigerant, and the most recent gauge readings).
    Ask yourself what could cause a system to lose a significant pressure difference between suction and liquid sides, and you'll be on your way to solving the problem. Without that pressure difference, the refrigeration cycle effectively ceases to exist.
    Jul 2001
    Blower speed?
    Lufkin TX
    Are the valves leaking by?
    Feb 2005
    Miami, Fl.