    By design, which of the following air ducts will allow 250 cfm to flow with a velocity of 500 ft/min?
    A. 9" x 8"
    B. 16" x 9"
    C. 10" x 9"
    D. none of the above
    a.
    Apr 2008
    How did you come up with that answer?
    Jun 2001
    Louisville, KY
    9*8/144 = 0.5 sf
    250 cfm / 500 fpm = 0.5 sf
    Volumetric Flow = Velocity * Area
    So, Area = Volumetric Flow / Velocity
    Perhaps you should have read the instructions before calling.
    CFM/velocity=duct area in sq ft.
    250CFM/500FPM=.5sqft, 144 sq in to a sq ft, so .5 times 144 =72 sq in. So 9 x 8 duct.
    I type too slow.