    We have no A/C!

    A little background on this call... Went here for a PM/startups. This unit had a bad LPCO. The way the contract was set up, NO repairs can be made on a PM without authorization. So, I noted it and left it (it wasn't warm enough to need it yet, anyway). Apparently, the tenant (a weight loss center) needed the cooling anyway (understandably). Since we are hired by the bldg. owner and not the tenants, they didn't know we were their service company, and called someone else. The landlord showed up while they were there, and kicked them out not thinking anything of it. Then we get an emergency call for A/C. This is what I found, only expecting to be replacing a LPCO, and having no idea another Co. had been out here. The funny part is, they had the transformer ripped out, and all the other wiring disconnected. What a mess. Got some nice overtime, though since I was sent at the end of the day, and it was supposed to be a quick fix. Had to rewire most of it, using a washed out, illegible wiring diagram.

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,755
    So where are the pics.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    401


    (Pic didn't come thru 1st time)

  4. #4
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    401
    Quote Originally Posted by beenthere View Post
    So where are the pics.
    Don't worry... I wasn't trying to take you "around the world" again.

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,755
    Did the landlord catch them trying to fix it.
    Or trying to strip it.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    401
    Trying to fix it, I guess.... but I don't understand why they had the transformer and half of the wiring out when all it needed was a LPCO. Apparently they had no clue where to start troubleshooting it, and just started replacing stuff randomly.

  7. #7
    Join Date
    Oct 2006
    Location
    In a freezer or in an attic somewhere
    Posts
    550
    Did it take you back to a/c basics? It is a transformer. Wire it and begone.

  8. #8
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    439
    looks like they bad the blower motor off as well. Seen it in the lower right hand corner.
    When you do a job, Always make it easier for the next guy, because you may be the next guy working on it.

  9. #9
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    401
    Quote Originally Posted by MichaelPaladin View Post
    looks like they bad the blower motor off as well. Seen it in the lower right hand corner.
    I didn't realize that was in the pic... we actually had that off because we had to replace the mount while we were there, too. My helper was working on that (his knee is in the pic, too) while I was working on the other mess.

  10. #10
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,755
    For some reason. Lots of guys don't think to check for safeties being open. They just start replacing any thing electrical that is in sight.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Mar 2008
    Location
    O'Fallon, MO
    Posts
    249
    LPCO? low pressure control something?

  12. #12
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    401
    Quote Originally Posted by matticus View Post
    LPCO? low pressure control something?
    Low Pressure Cut Out

  13. #13
    Join Date
    Apr 2008
    Location
    Pluto
    Posts
    983
    That transformer hanging there looks like the transformer bandit struck that unit. You'd be surprised how many of those I see hanging by their wires when I open up an air handler or some other...
    Not as lean, not as mean, but I'm still a hardcore, ass-kicking, hard charging Marine! Oohrah!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event