    Home Made Distributor

    Even though the TXV is sized properly, You cannot control the superheat in this coil. Someone removed the factory distrbutor and installed this. It killed the compressor. We just got done replacing the condensing unit and it was flooding back bad.
    Attached Images Attached Images    

  2. #2
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    401
    That's too funny...I didn't know Rube Goldberg himself was moonlighting as a refer tech!

  3. #3
    Join Date
    Nov 2003
    Location
    Boston
    Posts
    600
    Why go through all that time and trouble to make a distributor?
    It's got to be cheaper and easier to put in a factory made one.

    Looks like good quality work though.
    Edited by powerhead on more than one occasion

  4. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    What about it killed the compressor? Looks like it should work just fine...
    If more government is the answer, then it's a really stupid question.

  5. #5
    Join Date
    May 2006
    Location
    east central indiana
    Posts
    1,117
    Orignially posted by mark beiser
    What about it killed the compressor? Looks like it should work just fine...
    Kinda what I was thinking also...
    This space for rent.

  6. #6
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,339
    an adjustable TXV or a AEV maybe?? if your gonna try to band aid it instead of installing a new distributer
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

  7. #7
    Join Date
    Jun 2007
    Location
    Williamsport, PA
    Posts
    172
    Quote Originally Posted by beachtech View Post
    an adjustable TXV or a AEV maybe?? if your gonna try to band aid it instead of installing a new distributer
    That txv is ajustable. We spent some time trying to adjust the txv. No amout of adjusting the txv will make up for the absence of a distributor.

  8. #8
    Join Date
    Sep 2004
    Location
    Volunteer State
    Posts
    273
    I rebuilt this one a couple of years ago. It was still working as of the other day.




    This is the system's OD fan/coil unit.


    This thing was installed new in the mid-60's and is still cooling the building. Every now and then you have to get the rust out of the drain, but other than that, it works OK.

  9. #9
    Join Date
    Apr 2008
    Location
    Pluto
    Posts
    983
    I've actually done this myself on a few a/c units. While one was changed out a while back ago, the others are still working.
    Not as lean, not as mean, but I'm still a hardcore, ass-kicking, hard charging Marine! Oohrah!