    Quote Originally Posted by Tommy1010 View Post
    The fans would come on before the compressors.
    In resi, you don't want the fan coming on before the compressor.
    Many newer units the compressor comes on first, to allow the coil to get cold first.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,031
    Quote Originally Posted by beenthere View Post
    In resi, you don't want the fan coming on before the compressor.
    Many newer units the compressor comes on first, to allow the coil to get cold first.
    Ahh, I didn't know that. I been in commercial since I finished school. Thats great to know though. So after the T-stat is satisfied, does the fan stop with the compressor also? I'm assuming NOT. That'll only leave a cold coil useless and make it less efficient. Am I wrong again?

  3. #16
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    depending on what size your system is, the compressor will draw around 4 times as many amps as the blower

    that being said, your problem is most likely with the compressor

    can't go into more detail in this forum!

    a delay on make (for the compressor) will just raise the humidity level in your house in the cooling mode



    .

  4. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,758
    Many systems have a fan off delay.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #18
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Many systems have a fan off delay.
    i have never been a big "fan" of (fan off delay)

    a sequencer with a 15 second on/off delay works well

    when trane came out with the 90 second (fan off delay) many years ago, i was disappointed with the long delay

    most p.c. card and p.c. board delay relays have more delay than needed IMO

    which inheritently raises humidity during cooling mode


    .

  6. #19
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,758
    Yea, I think 15 seconds would be plenty in cooling mode.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event