    Confused What do you think?

    Made a sizable investment in a complete Trane XV80 Furnace and XR13 Heat pump system 2 weeks ago. AC failed about 2 days after install. After misdiagnosis- 4 service calls and a new line set- installer discovered TXV on the new indoor A-coil was bad. Installer wants to replace the TXV- is an entire new coil in my best interest? I was told pressure limit switches protect the system, but could other system damage have occured?

  2. #2
    Join Date
    Nov 2004
    Location
    North Carolina
    Posts
    443
    TXV only. That's all that's bad and you won't gain a thing by changing out the coil. Sometimes you just end up with a bad part when you buy something new and that's what the warranty is for.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,913
    Bad TXV won't cause any harm to the coil, so just a TXV is fine.

    Could it have damaged something else, doutbful it did, and if it did, it would show up when they installed the new TXV.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Apr 2008
    Location
    TEXAS
    Posts
    1,701
    ive never seen a bad txv damage a coil, but if it did your warranty would cover it.

  5. #5
    Join Date
    Dec 2007
    Location
    Ohio
    Posts
    2,875
    Bad TXV or no use of nitrogen while brazing in during the initial install?????




    ....Things that make you go.....hmmmmmmmm
    I need a new signature.....

  6. #6
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    677
    Quote Originally Posted by I_bend_metal View Post
    Bad TXV or no use of nitrogen while brazing in during the initial install?????




    ....Things that make you go.....hmmmmmmmm
    I am also thinking that there was no protection of the txv bulb during brazing either. Maybe not an equipment failure but an installer failure. It seems that I run across that more than actual warrenty failed parts or equipment.
    I am the "Wally". All others are meer imitations of the original.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  