Page 2 of 2 FirstFirst 12
Results 14 to 18 of 18
  1. #14
    Join Date
    Apr 2007
    Posts
    623
    Post Likes
    Thread Starter
    Quote Originally Posted by mark beiser View Post
    That wire isn't installed to code anyway.

    I agree about running conduit between the disconnect and units, and properly supporting the conduit. But the wire would also need to be replaced with something that is approved for running in conduit, which romex isn't.

    I even run my control wires in 1/2" sealtight between the wall and the unit. UV protected cable may protect it from the sun, but it offers no protection from weed whackers and dogs.
    Yeh the dogs especially, I had a customer once that wacked the low voltage wire on a heat pump, in an attempt to fix it they just stripped all the wires and spliced them all together into 1 wire nut. It was hard not to laugh when they told me they could just not understand why it wasnt working even though they "re-connected" the wire.

  2. #15
    Join Date
    Mar 2005
    Location
    Near Philly
    Posts
    98
    Post Likes
    I've got squirrels that chew on the liquidtight line for the line voltage. I have to replace it every few years as they expose the wiring to the elements.

  3. #16
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    14,366
    Post Likes
    Quote Originally Posted by powell View Post

    I'd definitely call the local authorities. Although they're probably aware of it.
    Installer told them it was the thermostat wire and they ran the power through the expensive copper conduit :eek
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  4. #17
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes
    On top of everything, I like to use stranded wire between disconnects and units, that goes for any machine with any sort of vibration.
    ___________________________________________


  5. #18
    Join Date
    Apr 2008
    Location
    Toronto, Canada
    Posts
    166
    Post Likes
    wow. that wiring is unbelievable. in toronto we dont need permits for AC replacement and so this kind of thing is possible. you'd think an hvac guy would know better. maybe that was a diy job or something?