How do dampers affect velocity and flow?
Hopefully someone can enlighten me ...
Dampers are used to control the volume of air that enters a branch, but how do they affect velocity? I would assume the air speeds up as it flows through the damper opening, but would then slow back down after continuing down the branch.
Here's the problem ...
I have a room that requires 57CFM of cooling according to manual j. It calls for a 4 inch duct at 600fpm. Everyone I talk to recommends using a 6 inch and installing a damper, but with 57cfm in a 6 inch duct; velocity will drop to 300fpm which will not allow proper room mixing. Should I just resize the register to increase velocity, use the 6 inch duct or go with the manual d recommended 4 inch???
I'm having the same issues on other outlets calling for 5 inch, 3 inch, etc. Should I go with the so-called experts or the manual d/j????
Thanks.
Jack
-
05-05-2008, 11:00 PM #2
Who are the "experts" you are refering to? 57 cfm with a 6"? A little overkill.
Jim
-
05-06-2008, 06:52 AM #3
Professional Member
- Join Date
- Feb 2003
- Location
- Huntsville,AL
- Posts
- 4,125
one would be hard pressed to measure the effects from the normal designed damper for HVAC residential ducts -- so far as causing flow problems --
are you still in the design stage?
many installers will just use 1 size duct, then add dampers --harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!
-
05-06-2008, 07:30 AM #4
You'll have some turbulance right at and after the damper. But if your register isn't within 2' or so of the damper no problem.
For a room requiring 57 CFM, I would use a 5" and damper. Depending on length of the run. You'll be hard pressed to find 3" pipe. I don't use anything less then 5". On jobs that only have one supply that would size out less the 6" inch, quite often we use just 6" and a damper for that one run. If all supplies are sized to the FR that the Manual D said to use for the duct system, very few supplies come to less then 5".
Select registers and grilles for the throw you need.
-
05-06-2008, 08:45 AM #5
Regular Guest
- Join Date
- Feb 2008
- Posts
- 11
-
05-06-2008, 09:08 AM #6
-
05-06-2008, 09:17 AM #7
-
05-06-2008, 08:48 AM #8
Regular Guest
- Join Date
- Feb 2008
- Posts
- 11
-
05-06-2008, 08:44 AM #9
Regular Guest
- Join Date
- Feb 2008
- Posts
- 11


Reply With Quote