Results 1 to 9 of 9
Thread: FX 16 Remote Display Problem
05-03-2008, 03:23 PM #1
- May 2003
- Connecticut
- 450
I have an FX 16 with onboard display. I am trying to add a remote display. I have it hooked up to the remote display terminals but it just says device offline and address 1. I tried changing addresses and re-downloading the configuration but it doesn't work. I also noticed that it says RT+ RT- and RT Com so I tried hooking it to the local bus. It still doesn't work. any ideas anyone??
05-04-2008, 02:58 PM #2
- Apr 2007
- Russia
- 33
only onboard display will work if you have it on controller.
You can remove it then try to connect remote dispay everything will be ok
05-04-2008, 03:19 PM #3
- May 2003
- Connecticut
- 450
That is not what johnson is saying. I have a call in and they are trying to find the answer.
05-04-2008, 03:25 PM #4
- May 2003
- Connecticut
- 450
I just read the manual and it says you can have the onboard and up to 2 remote displays on an fx16
05-05-2008, 03:06 AM #5
- Apr 2007
- Russia
- 33
remove the onboard display and you will see
05-05-2008, 05:14 AM #6
- May 2003
- Connecticut
- 450
I already did with no change.
05-05-2008, 09:30 AM #7
- Apr 2007
- Russia
- 33
Do you have any configured data on display string or value?
05-05-2008, 10:02 AM #8
- Jun 2006
- Athens Greece
- 108
Can you check that the MUI version is aligned with FX FW version and your tool version?
05-05-2008, 04:00 PM #9
- May 2003
- Connecticut
- 450
Johnson called back today and told me after the download to cycle power. it works like a charm now.