    mini split troubles

    hey guys iv got a question for ya. iv got a mini split here that im having a problem with. for some reason i cant pull a vaccum on the system past 1000, so i charged with nitrogen to find the leak to 150 low side and it held for an hour no fluctuations at all also soap checked all fittings and no leaks. i put a micron gauge on the pump itself and it pulls past 400 so i know its not the guage or vaccum but i still cant pull past 1000, 1500 on the sysytem so here is where you guys come in any suggestions?

  2. #2
    Join Date
    Apr 2008
    Location
    ireland
    Posts
    11
    Hey stomper

    Your pump should pull down to at least 50microns.

    I'd try changing the oil in the pump or

    If your using an electronic gauge, the sensor may need to be cleaned.

    I,d try checking the above before worrying about system.

    Kev.

  3. #3
    Join Date
    Apr 2008
    Location
    Central CA
    Posts
    566
    pump gets fresh oil on every startup and drained 5 min after turnoff il try cleaning the sensor
    by the way pump does pull down to 50 i was just making sure the gauge would even read past 1000 thats why i only went to 400

  4. #4
    Join Date
    Apr 2008
    Location
    ireland
    Posts
    11
    Okay,

    So pump and sensor are fine.

    Did you try holding vaccum when you got to 1000 microns. Possible leak maybe.

    or

    If your certain theres no leaks there could be moisture in the system.

    What kind of system are we talking about?

  5. #5
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    try doing a triple vac purging with nitrogen, hoses or gauges leaking?

  6. #6
    Join Date
    Jan 2008
    Location
    Montreal, Canada
    Posts
    41
    have you checked the hoses/manifold you are connecting the pump with?
    have you checked the valves on the unit to be sure they are closed(ran into this once.)?

  7. #7
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,478
    How long did you leave the pump on there?

    Mini's seem to take forever to pull down sometimes.