    Confused 30 HXC medium brine option not installed ???need help from carrier tech

    Hi ,

    We recently came across a new client .

    He have 4 30 hxc chiller ,two of them we're supposed to have brine option..

    Looking at the model number the two last letter are AA not LA.

    LA stand for brine option

    The compressor discharge superheat is high between 40 -70 F
    And the system look like is missing some gas.

    What is the brine option?
    Is it field modifiable ..i.e: orifice size in EXV?

    Thanks

  2. #2
    Join Date
    Jul 2005
    Location
    south
    Posts
    699
    Post Likes
    modified programming allowing chiller to run lower temperatures(with addition of glycol) than a chiller designed for comfort cooling

  3. #3
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    Thread Starter
    My main concern ain't the programming.
    We've modified the chiller to run on medium brine safety and run to lower temp.

    The problem is glycol ain't the same as water for heat exchange.

    Gpm is ok vs design pressure drop value.But the discharge superheat is around 40 to 70 F ,which is high.
    Discharge superheat target is 22 F.

  4. #4
    Join Date
    May 2006
    Location
    Mooresville, North Carolina
    Posts
    231
    Post Likes
    I wouldn't worry about the discharge supperheat too much. Just make sure the EXV is below 60%. The brine option includes solenoid valves in the liquid lines and depending on the size smaller orfices in the EXV. There are wires in the wiring harnes that can be used to to control the liquid line valves, but may actually be faster to run your own. The orfices you will have to get from Carrier. Sorry, I don't work for them anymore so I can't get the numbers. Good luck.
    Refer all arguments to the wife, she's better at it.
    www.fairtax.org

  5. #5
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    The unit can be field modified what is your designed leaving water temperature ?

  6. #6
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    Thread Starter
    The chiller as been designed for 33.5 F

  7. #7
    Join Date
    Jan 2012
    Location
    Dallas
    Posts
    597
    Post Likes
    Quote Originally Posted by patpinet View Post
    My main concern ain't the programming.
    We've modified the chiller to run on medium brine safety and run to lower temp.

    The problem is glycol ain't the same as water for heat exchange.

    Gpm is ok vs design pressure drop value.But the discharge superheat is around 40 to 70 F ,which is high.
    Discharge superheat target is 22 F.
    Am I missing something ? How's more heat removal (heat exchange) gone lower your discharge superheat. I must be missing something

  8. #8
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    Thread Starter
    Quote Originally Posted by jman2794 View Post
    Am I missing something ? How's more heat removal (heat exchange) gone lower your discharge superheat. I must be missing something

    Basically by helping evaporate the liquid refrigerant in the evaporator.

    Less heat exchange could relate to less mass flow of refrigerant coming back to compressor.

  9. #9
    Join Date
    Jan 2012
    Location
    Dallas
    Posts
    597
    Post Likes
    Oh. I assume you running high superheat too. I believe somebody had asked what the EXV % POSITION IS? I'm not trying to take over your thread just trying to wrap my head around it

  10. #10
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    Thread Starter
    No problem, I'm trying to help the people that are helping me too

    This compressor is sitting on the barrel so basically there's no superheat that can be taken.

    The exv are at 100 and the condensor seem to be empty of gas as sight glass is bubbling.

    Lirunaway as said earlier in the thread that sometime carrier adding a smaller orifice in the exv probably to prevent shortage of gas I the evap.


    As for the thread thanks to everybody for you're help.

  11. #11
    Join Date
    Jan 2012
    Location
    Dallas
    Posts
    597
    Post Likes
    Thanks very much

  12. #12
    Join Date
    Jan 2012
    Location
    Montreal, Canada
    Posts
    158
    Post Likes
    Quote Originally Posted by patpinet View Post
    Hi ,

    We recently came across a new client .

    He have 4 30 hxc chiller ,two of them we're supposed to have brine option..

    Looking at the model number the two last letter are AA not LA.

    LA stand for brine option

    The compressor discharge superheat is high between 40 -70 F
    And the system look like is missing some gas.

    What is the brine option?
    Is it field modifiable ..i.e: orifice size in EXV?

    Thanks
    You might have to speak to Antonios . He followed a training at Carrier last month or even Dennis he is a damn good tech. Maybe Gweltaz or Etienne too. 😉

  13. #13
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    670
    Post Likes
    Thread Starter
    I'll try with Dennis he received some screw training recently. 😀
    Probably he's got some good answers

  14. #14
    Join Date
    Jan 2012
    Location
    Montreal, Canada
    Posts
    158
    Post Likes
    👍

  15. #15
    Join Date
    Aug 2011
    Location
    Chicago
    Posts
    64
    Post Likes
    Converted a 30GX air cooled outdoor unit to Ice Rink duty. Had to replace expansion valve orifices on electronic EXV housed in economize also selection for brine only allowed unit to go to 18 degrees (HXC will do -0 if selection is done properly). Had to put resistors in to have 18 degrees = 8 degrees. However the major issue was GPM through evaporator unit required 500 GPM for 44 deg fresh water for glycol with a -10 rating GPM I was told I needed 1000 GPM. Well I had a little over 500. Customer and IceRink package distributor refused to address problem. Blamed issue on Carrier Chiller I was running 14 degree leaving brine with a -10 evaporate temp. A true cluster **** when a customer buys a third party assembly and manufacturer of one piece of equipment is expected to make it right and do on "Warranty"

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •