Thread: calculating gpm through chiller barrell

  1. #1
    Join Date
    Jan 2001
    Location
    Carlisle, Pa
    Posts
    945
    Post Likes

    calculating gpm through chiller barrell

    I have pressure gauges on supply and return of evap chiller barrel. how do I calculate gpm through chiller barrel to make sure it meets charts.

  2. #2
    Join Date
    Jan 2007
    Posts
    23
    Post Likes
    Use pressure differential and the manufacture's chart. This pressure drop will correspond to a specific water flow for that manufacture.

  3. #3
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    727
    Post Likes
    Like stated above, use manufacturers flow chart. If you don't have one, you can use this equation : ^T(delta) x gpm / 24 = Tons. You've got tons & delta, ^T / 24 x tons = gpm. There is one which involves square root for ACTUAL gpm....can't remember it though. Your gauges are there to determine not just pressure, but ft. of head. (1 psig = .433 ft) this will help show if the pump is putting out properly. The equation above is more rule of thumb, but it is helpful. Hope this can help.
    Sic Semper Tyrannis.

  4. #4
    Join Date
    Apr 2005
    Location
    Niagara Falls,NY
    Posts
    93
    Post Likes
    1 psig=2.31 ft head /you need the chiller spec sheet to find out design gpm and pressure drop thru barrel then you take the actual pressure drop thru barrel and plug it into formula: design gpm multiplied by square root of actual pressure drop divided by design pressure drop

  5. #5
    Join Date
    Nov 2004
    Posts
    221
    Post Likes
    Quote Originally Posted by wonder_boy View Post
    1 psig=2.31 ft head /you need the chiller spec sheet to find out design gpm and pressure drop thru barrel then you take the actual pressure drop thru barrel and plug it into formula: design gpm multiplied by square root of actual pressure drop divided by design pressure drop
    i agree with wonderboy,very well put and 1psi=2.31 ft hd and 1 ft hd = .433 psi. good luck

  6. #6
    Join Date
    Dec 2003
    Location
    45th Parallel
    Posts
    1,036
    Post Likes
    only use one guage to take supply and return pressure readings.
    If possible manifold supply and return to one guage using valves to isolate, or use petes plugs to take readings.
    Never use two separate guages, not if you want accurate readings.

  7. #7
    Join Date
    Feb 2006
    Posts
    226
    Post Likes
    dont forget to subtract or add for difference in elevation of two points of measurement

  8. #8
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    you can also get the pressure differential through the pump and check the pump curve.

    good luck.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •