    NAVIEN COMBO 180 BOILER issues

    Ignition failure code on a newer unit natural gas correct pressures.
    Anyone else have issues with these units ?

  2. #2
    Join Date
    Nov 2004
    Posts
    1,438
    Post Likes
    More info is needed.

  3. #3
    Join Date
    Jan 2015
    Posts
    1
    Post Likes
    I saw a gentleman on linkin by the name of Chris Staley who is friends with I belive everyone that's works @ Navien. His list of specialties one being a Navien service specialist. He posted a long to some website I beleive to be his just by reading it and looking at the pics on the website (by the way I do believe it was some of the best Navien installs I have ever seen). What I'm getting @ is their is a place to email him questions or comments. Maybe try there. Here is the link I found
    http://cstaleyofregalincpics.page.tl/ Hope this will help you

  4. #4
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    2,388
    Post Likes
    more info is needed. Most Tankless units I've serviced that were having problems were usually caused by installer error. Most common problem is undersized gas line.

  5. #5
    Join Date
    Jul 2003
    Location
    Rochester NY
    Posts
    162
    Post Likes
    Thread Starter
    Hi guys thanks for the replys. It was 0 deg weather the week this unit had problems.
    It has a dedicated 3/4 black pipe gas line.
    The gas meter on the house is very very old and is getting replaced by the utility company.
    I had correct gas pressure of 3.5 inches.
    Its been running fine with warmer temps. The ventng is correct too with the intake pipe and vent pipe spacing correct.

  6. #6
    Join Date
    Jun 2004
    Location
    EXIT 16W www.wmtandson.com
    Posts
    5,179
    Post Likes
    would help if you described the "issues"
    Quote Originally Posted by rob air View Post
    Hi guys thanks for the replys. It was 0 deg weather the week this unit had problems.
    It has a dedicated 3/4 black pipe gas line.
    The gas meter on the house is very very old and is getting replaced by the utility company.
    I had correct gas pressure of 3.5 inches.
    Its been running fine with warmer temps. The ventng is correct too with the intake pipe and vent pipe spacing correct.
    DON"T mess with the US
    I thought I had been there and done That.
    ITS ALL ABOUT LEARNIN!
    I thought it would be better by now
    "He who works with his hands is a laborer.
    He who works with his hands & his head is a craftsman.
    He who works with his hands, his head & his heart is an artist."
    ~St. Francis of Assisi

  7. #7
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    Quote Originally Posted by rob air View Post
    Hi guys thanks for the replys. It was 0 deg weather the week this unit had problems.
    It has a dedicated 3/4 black pipe gas line.
    The gas meter on the house is very very old and is getting replaced by the utility company.
    I had correct gas pressure of 3.5 inches.
    Its been running fine with warmer temps. The ventng is correct too with the intake pipe and vent pipe spacing correct.
    You're painting with a very broad brush my friend.
    3/4" line means nothing without length.
    Are you a homeowner or tech?
    "The only true wisdom is in knowing you know nothing" Socrates

  8. #8
    Join Date
    Oct 2013
    Location
    Alberta Canada
    Posts
    514
    Post Likes
    Quote Originally Posted by rob air View Post
    Ignition failure code on a newer unit natural gas correct pressures.
    Anyone else have issues with these units ?
    Had a ton of issues on the first gen, second gen and beyond were much better.

  9. #9
    Join Date
    Jun 2004
    Location
    EXIT 16W www.wmtandson.com
    Posts
    5,179
    Post Likes
    Ignitor?
    flame sensor?
    could be lack of maintenance
    Quote Originally Posted by Linktorn View Post
    Had a ton of issues on the first gen, second gen and beyond were much better.
    DON"T mess with the US
    I thought I had been there and done That.
    ITS ALL ABOUT LEARNIN!
    I thought it would be better by now
    "He who works with his hands is a laborer.
    He who works with his hands & his head is a craftsman.
    He who works with his hands, his head & his heart is an artist."
    ~St. Francis of Assisi

  10. #10
    Join Date
    Dec 2006
    Location
    toronto, canada
    Posts
    605
    Post Likes
    If you got 3.5" gas pressure on a Navien unit, you are having problem. Cause for inlet, 3.5" is not enough. For outlet, newer model should be negative because the inducer suck in the gas and air; for old model, you have to follow their instruction on how to set gas pressure, you cannot just measure the manifold pressure.

  11. #11
    Join Date
    Dec 2006
    Location
    toronto, canada
    Posts
    605
    Post Likes
    Maybe you can try this one. http://us.navien.com/Content/Attache.../NCB/main.html
    This for newer model.

  12. #12
    Join Date
    Dec 2006
    Location
    toronto, canada
    Posts
    605
    Post Likes

  13. #13
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Quote Originally Posted by rob air View Post
    Ignition failure code on a newer unit natural gas correct pressures.
    Anyone else have issues with these units ?
    The CH180 models will not work for more than a day when cold on propane. The NCB210 is fine.
    No way to fix the issue either.
    Quality and Value Service and Repair

  14. #14
    Join Date
    Feb 2014
    Location
    Connecticut
    Posts
    64
    Post Likes
    I had a ch180 LP unit that we kept getting the same error. According to Navien they have had ongoing issues with the ch180. They ended up replacing it with a ch210 and there has not been anymore issues. Supposedly the ncb180 has no problems with Navien having changed to a negative pressure gas valve.


    Sent from my iPhone using Tapatalk

  15. #15
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Never heard of a good one yet
    Quality and Value Service and Repair

  16. #16
    Join Date
    Aug 2014
    Location
    Oxford, Massachusetts, United States
    Posts
    5
    Post Likes
    What is your dynamic vs static pressure

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •