Results 1 to 13 of 36
    Apr 2008
    Need help: Noisy air flow with new heat pump system
    I just got rid of the old fuel oil furnace for heatpump with electric backup. The noise and draft from the extra air movement was unexpected and now I'm wishing I would have kept the old system. Would I have been better off to go with propane or back to fuel oil? Is there something I can do to correct this? With my old system I couldn't even here it run. I have a 4 ton goodman system with vairiable speed motors.
    You can't get the company that installed it to come back?
    Call the contractor back, to come and check it out.
    If the ducts are too small, then he needs to tell you what it will take to fix the duct system.
    Was a load calc done, or did they just size it off the sq ft of your house.
    What size A/C system did you have before??
    Sonuds like the ducts are undersized or the fan is set to high.
    Apr 2008
    He came out and looked at my ductwork before I ordered . My house is 1500sq ft not including a full finished basement. My old cooling sytem was rated at 3000btu. I'll have to have him come back out. With most new systems now, do they move more air because the heat doesn't get as hot? With my old system I couldn't even hear when it turned on for cooling or heating. Should it be that way with the new system? Thanks for the replies.
    Do you mean 30,000 BTU's for the A/C?
    Sounds grossly oversized for 1500 sq ft.
    How many estimates did you get for this replacement.
    Apr 2008
    It is a 10 seer rheem for cooling but the coil in the old furnace said 3000btu. When figuring my sqft do you include the basement so instead of 1500 it would be 3000. He said I had to go with a 4ton because it wouldn't be enough heat for here in Minnesota. It would be on the backup heat too often. I can't find anything for size on the old air conditioning unit but I think the heat pump was sized more for heat. I had three bids for the project, 2 bid 4 ton, 1 bid 3 ton.
    Dec 2006
    Middle Tennessee
    Do you mean 30,000 BTU's, Sounds grossly oversized for 1500 sq ft..
    nah, but they probably replaced the 2-1/2 with a bigger system!
    i would have the co. who put it in come back and check duct sizes and also blower speed. as for the heat pump i'm assuming where you live in minnesota it gets very cold, i'm n ot a fan of heat pumps in extremely cold temps even with electric heat.
    Gasp! 4 ton for 1500 sq ft, no wonder it is noisy. Going from 2.5 to 4 ton on the same duct system? No wonder it is noisy. What brand is it? Oh yea...
    Sorry, you have a real mess on your hands.
    DC Metro Area (MD)
    Ask the contractor who sold you the system to do a load calc. to prove his sizing technique, if he stands behind his work.
    Is the basement actually conditioned (heated/cooled)?
    Heat pumps are typically sized for cooling, not heating.
    Jun 2001
    Louisville, KY
    Me thinks his installer doesn't understand air flow and duct sizing.