    Question rtac with ch-530 controls

    a good customer has numerous rtac chillers with ch-530 controls,after a
    recent rain storm one of the ch-530 screens was blank, when it was removed
    water ran out of it. has anyone had this problem?, if so how was it fixed?

  2. #2
    Join Date
    Jul 2004
    Location
    Parkersburg WV
    Posts
    345
    You can try drying it out with a blow dryer and reinstalling, but I would suggest just replaceing it with a new one, when you order the new one Trane sends a new gaskest to seal it with, just make sure your surface is clean when applying the new part, if you want added protection I guess you could also caulk around then unit or even build a hood/rain shield out of sht metal and put around it, just be aware of the condensor coil and wiring behind it.

    I am also assuming your have the software needed to configure the controller.

    Hope this helps.
    Work smarter not harder.