    Set me straight here guys.

    Say the thermostat WAS "short cycling" the compressor...........wouldn't the overload on the compressor kick out long before the breaker tripped? Even with repeated LRA start attempts one would think the overload would take it in the shorts long before the breaker did.

    Hvacmd - you said the amp draw at the panel was 12.4 - was this the same amp draw you got when you checked it at the unit?

    I had a True freezer defrost issue a couple years ago. Turns out one of the wires inside the back wall of the cabinet short to ground. How this happened I have no idea........but it happened.

  2. #22
    Join Date
    Apr 2008
    Location
    Southern New Hampshire (USA)
    Posts
    402
    Post Likes
    I can second Executioner..... we had a True freezer tripping the breaker as well... it was a GFI circuit, and upon calling True, they told us that the freezer should not be connected to a GFI circuit because it will trip it. Of course, this is just stupid, since all new construction around here is requiring ALL kitchen circuits to be GFI, but it is what it is.

  3. #23
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by markettech View Post
    I had a True freezer defrost issue a couple years ago. Turns out one of the wires inside the back wall of the cabinet short to ground. How this happened I have no idea........but it happened.
    I've had the orange two wire defrost heater safety screwed to the ceiling shorted more then a few times on these boxes but, you could detect the short by meg ohms at the wall plug? hvacmd2002 did you check with a megar at the plug?
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  4. #24
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Quote Originally Posted by nightranger121 View Post
    I can second Executioner..... we had a True freezer tripping the breaker as well... it was a GFI circuit, and upon calling True, they told us that the freezer should not be connected to a GFI circuit because it will trip it. Of course, this is just stupid
    Is this possible? Wouldn't there have to be a short (problem with the unit) for the GFI to trip? I can't think of another unit besides an under counter Delfield that won't work on a GFI. They got the mullion evaporator dripping onto the evap fans and all the wiring
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #25
    Join Date
    Apr 2019
    Posts
    1
    Post Likes
    I have experienced this twice where intermittent circuit breaker Trips were occurring and multiple techs could not find problem. The compressor was very hot. I opened the expansion valve one turn on both. Had frost right up to the compressor body. Possibly the compressor was cycling on overload. Both have not tripped again.

  6. #26
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Cool story bro

  7. #27
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,750
    Post Likes
    Quote Originally Posted by Cosmo 8000 View Post
    I have experienced this twice where intermittent circuit breaker Trips were occurring and multiple techs could not find problem. The compressor was very hot. I opened the expansion valve one turn on both. Had frost right up to the compressor body. Possibly the compressor was cycling on overload. Both have not tripped again.
    Did you check the SH after adjusting?

    BTW you replied to a 11 year old post!

  8. #28
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    is this a dedicated circuit?

    nothing else on it?

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •