Results 1 to 3 of 3
  1. #1
    Join Date
    Mar 2008
    Posts
    103
    Post Likes

    RTAA- History Memory Error Type 1 Message

    Got a call to troubleshoot RTAA chiller. Faults are
    1) History Memory Error Type 1
    2) Compressor Overload Setting Alarm
    Haven't worked on RTAAs before and am digging up manuals. Any heads up advice on these faults. Heard I might have a board failed.

  2. #2
    Join Date
    Oct 2007
    Location
    Eastern N.C.
    Posts
    147
    Post Likes

    RTAA memory error

    the book says ucm is operating on ROM default for all setup parmeters. check all setup parameters and continue to run chiller. the default overload setting must not match the dip swich settings. you can get the IOM from the trane web site RTAA-10M-4A. If the settings don't stay in the module then a replacment will be needed.

  3. #3
    Join Date
    Mar 2008
    Posts
    103
    Post Likes

    RTAA Memory Error

    PJ's cool-aid
    Thanks. Got the manual and info I needed.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Quality Home Comfort Awards