    New Boiler Continually Shutting Off - I'm freezing......!

    Hi, I've recently had a new boiler installed and had the exhaust lined with 6" flexible liner to update the heating in my home. The safety on the doiler keeps tripping every 20-30 minutes. My HVAC guy has no answer other than he thinks the exhaust liner needs to be increased from 6-7"

    Bottome line is I've done what I could and I'm still not able to heat my house. Let me provide the details. Please give me some honest advice if you can. Thanks.

    I live in an 1850 row house in Baltimore that was in pretty sad shape when I purchased it a few years ago. The boiler was circa 1930 and the exhaust dumped into an unlined chimney. Well the chimney collapsed, causing the smoke to vent into the 1st floor instead of up and out of the chimney.

    I had the chimney lined and the contractor used a 6 inch flexible liner. It is about a 35 foot run up from the basement to the top of the chimney. A new furnace was installed a few weeks later, so now I have the following pieces of equipment exhausting up through this 6" liner.

    Smith Boiler Model# GB 100-W-5-INTO
    Normal Input 100,000 BtU/hr
    Normal Output 83,000 BtU/hr

    Rheemglas Imperial Water Heater Model # 22A1-402-1
    Normal Input 38,000 BTU/hr
    Normal Output - Not available

    So after the new boiler was installed in late Feb last year everything went well. The boiler did shut off a few times for some unknown reason, but by an large everything ran smoothly through the latter half of the winter and the spring.

    Within the last 3 months, the safety on the boiler has begun to trip out regulary. I would reset the boiler, and it would run for a day or longer at first, and more recently, it trips out every 20-30 minutes.

    My HVAC guy suggested that the problem is that there are too many BTU's exhasuting out of my boiler and water heater. I countered with if that was the case then it should have occured last year as well.

    To test this theory we shut off the water heater and the the boiler ran for about a day before it again tripped the safety. I am now back to resetting the boiler every 20-40 minutes in an effort to get the house to stay at even 60 degrees.

    HVAC then suggested that their is a constriction of some sort in the exhaust tube, such as a bird etc or an internal collapse which has kinked the flexible exhaust piping. The top of the exhaust is capped so there is no opportunity for anything such as a bird to fly into the liner. I checked from the top down and I can see a collapse so I'm assuming the liner is undamaged.

    Could this be a cause for a larger liner. If yes, why wasn't this a problem for 3-4 months last year.

    If this is not the case, does anyone have any suggestions as to what could potentially be the cause of the safety continually tripping on this 1 yr old boiler?

    Help Please!

    Thanks.
    Last edited by gojojo67; 04-03-2008 at 10:36 AM.

  2. #2
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Post Likes
    "I checked from the top down and I can see a collapse so I'm assuming the liner is undamaged."

    What exactly do you mean by this statement? The chimney has collapsed but the liner hasn't? There are a number of reasons the boiler will trip out. High temp, low water, flame failure, just to name a few. Am I correct in assuming your tech has considered all of those possibilities before he blames the stack?

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    How are you resetting it.
    Turning power off then on, or a reset button.
    If a button, what button.

    A 6" Z Flex liner is listed as capable of handling your boiler and water heater total BTU.

  4. #4
    Join Date
    Apr 2008
    Posts
    8
    Post Likes
    Thread Starter
    Thanks for your response.

    I am positive that the integrity of the liner has not been compromised. The bricks had collapsed and prior to the liner being installed were reset. So I don't think that that is the problem.

    What the technician has checked I am not sure of. I will ask him if he has check any or all of these items. Its almost to the point where I am not sure of exactly how interested he is in pursuing this much further

    I am by no means mechanical with regard to HVAC, but what I find so puzzling is that the funcationality of the boiler has dwindled to almost nothing.

    Thanks.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    So how are you resetting it?

  6. #6
    Join Date
    Apr 2008
    Posts
    8
    Post Likes
    Thread Starter
    I'm resetting a button on the lower front of the boiler. Its set back about 6 inches into the unit. I have to reach in and up a bit to find the button. Do you suggest resetting the entire boiler? If so, I'll have to check the manual for that process.

  7. #7
    Join Date
    Feb 2008
    Posts
    1,274
    Post Likes
    I wouldn't just keep resetting that switch all the time, there is a reason it is tripping and although it may be safe enough to reset once or twice it sounds like it is doing its job and something is not right. Get an experienced set of eyes on the unit.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Is it a button thats about in the middle of a plate that is angled out toward you?
    If so, its the flame rollout switch.

    Cold be that its burning dirty and the boiler is clogged.
    The spill switch usuaslly trips before the roll out if its the chimney becoming restricted.
    And I think on your boiler, your spill switch is non resettable.

    Your contractor should check the boiler to see if it needs cleaned.
    He should also check the draft with a draft guage.

    You may have to call another contractor, it doesn't sound like youor current one, knows a lot about repairing/correcting boiler problems. JMO

  9. #9
    Join Date
    Apr 2008
    Posts
    8
    Post Likes
    Thread Starter
    I see that you're in Lancaster. I'm in Baltimore. Why don't you drive down and help me out. Haha.

    Yes, it is the button that is angled out towards me.

    Anyway, is it really possible that it could become clogged in less than 4-5 months of constant usage?

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Unusal, but more then possible. NG doesn't usually have this problem, but LP does it quick.

    Burners may never have been set up right. It doesn't take impingment long to cause trouble.

    Anything else done recently in the home.
    New bath fan, windows, doors, weather stripping.
    Anythin, even if you don't think it could effect the boiler.

  11. #11
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    It can become clogged over night.

    The switch is there to protect the lives of the people living in the building when a boiler or furnace that isn't correctly adjusted makes soot and plugs up.

    Look at the test results on the paper that he left, that shows CO2, CO, Draft, Gas pressure (inlet and outlet), and maybe O2.

    Let us know what the numbers are.

    Noel

  12. #12
    Join Date
    Apr 2008
    Posts
    8
    Post Likes
    Thread Starter
    I installed a couple of new windows a few weeks on the 3rd floor but this problem was already well established by then.

    I appreciate you input. Any last advice? It sounds as if my current guy is not the right guy to address this issue any longer.

  13. #13
    Join Date
    Apr 2008
    Posts
    8
    Post Likes
    Thread Starter
    One last comment. My HVAC keeps saying it must be the liner. He indicates that per his calcualtions and everything he has read, the exhaust ducting need to be increased for runs in excess of 20 feet. Any vailidy to his claim based on the original BtU outputs I listed int he original posting?

    Thanks Again.

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Accong to the Z Flex liner chart I have in front of me.
    6" liner can handle 213,000 BTU's at a 35' chimney height.
    By code, if your water heater has a 3" hood, it can't be vented into a chimney that has more then 49 sq inches area.

    If your installer read the install instructions(which I doubt), he would know that HE was suppose to verify if the chimney was sized right or not before he installed the boiler.

    Draft readings would be nice.

    I think you need another contractor.
    Screen them on the phone. Let them know them problems your having, so they can bow out gracefully if they don't know how to check everything.

  15. #15
    Join Date
    Apr 2008
    Posts
    8
    Post Likes
    Thread Starter
    No readings available, go figure.

    Appreciate the confirmation on the EZ liner load capacity.

    I will start looking for a new HVAC guy. Too bad, I need two new AC units installed as well. Looks like he will lose out on those as well.

  16. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Maybe its a good thing that the boiler problem is happening now instead of a year from now.

  17. #17
    Join Date
    Apr 2008
    Posts
    8
    Post Likes
    Thread Starter
    Yea, I guess thats one way of looking at it.

    Thanks again.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •