    Accong to the Z Flex liner chart I have in front of me.
    6" liner can handle 213,000 BTU's at a 35' chimney height.
    By code, if your water heater has a 3" hood, it can't be vented into a chimney that has more then 49 sq inches area.

    If your installer read the install instructions(which I doubt), he would know that HE was suppose to verify if the chimney was sized right or not before he installed the boiler.

    Draft readings would be nice.

    I think you need another contractor.
    Screen them on the phone. Let them know them problems your having, so they can bow out gracefully if they don't know how to check everything.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Apr 2008
    Posts
    8
    No readings available, go figure.

    Appreciate the confirmation on the EZ liner load capacity.

    I will start looking for a new HVAC guy. Too bad, I need two new AC units installed as well. Looks like he will lose out on those as well.

  3. #16
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,562
    Maybe its a good thing that the boiler problem is happening now instead of a year from now.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #17
    Join Date
    Apr 2008
    Posts
    8
    Yea, I guess thats one way of looking at it.

    Thanks again.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event