    New A/C compressor start up question.
    Installed new A/C system this winter. Installer put off checking system until the weather warms up in washington dc. My question is what type of test/s/ should the installer make to insure the correct amount of refrigerant was added to the system. From reading prior posts it appears just measuring the system with gagues does not appear to be enough. The unit is an infinity 4 ton compressor paired with an infinity gas furnace . Thanks
    Quote Originally Posted by ron3637 View Post
    Installed new A/C system this winter. Installer put off checking system until the weather warms up in washington dc. My question is what type of test/s/ should the installer make to insure the correct amount of refrigerant was added to the system. From reading prior posts it appears just measuring the system with gagues does not appear to be enough. The unit is an infinity 4 ton compressor. Thanks
    CFM of air flow will be established first.
    Pressures and temperatures will be established to meet Mfg. specs.
    Line voltage and load voltage, along with amperage will be established to be within specs.
    Condensate drain line will be tested.
    System capacity will be verified, and documented.
    I applaud you for choosing a contractor who is going about it the right way. If he has informed you that he needs to wait until its warm enough to test correctly, you dont need to worry about his procedures. He knows what he is doing.
    Quote Originally Posted by flange View Post
    Thats not 100% true.
    Good chance he's a quality contractor. But not a 100% guaranty.
    100% guaranty
    Springfield, Virginia, United States
    tests?
    good superheat
    good subcooling
    trust your hvac guy or find one you do
    good choice w/ infinity... smart man/wo