    Apr 2008
    Question Automatic Expansion Valves
    How do they work, what's the purpose of the adjusting screw, is it a good or bad valve, what's the position of the vale when in the off cycle?
    Western NC
    I won't go into a great deal of detail as you are a new member and I don't konw your qualifications.
    Basically, an Expansion Valve is a type of metering device that maintains a constant superheat as per the manufacturers specifications. There is a sensing bulb on it that connects to the powerhead and the powerhead in turn opens and closes a diaphram to regulate and maintain the superheat.
    Adjustable Expansion valves are used typically in commercial applications and allows the technicain on site to adjust the superheat to acheive the manufacturers specifications.
    There are advantages and disadvantages to the adjustable. Biggest advantage is the expansion valve can be used on any brand system for its rated size. And since most manufacturers have their own superheat specs., it can easily be adjusted to reflect that. Biggest disadvantage is if the technician does not know its an adjustabe of if the technician is not familiar with how to adjust them, problems could be encountered.
    Apr 2004
    In refrigeration the term "automatic expansion valve" normally refers to a valve used to maintain a constant outlet pressure such as an evaporator pressure requlator. The stem in this case would be the pressure setting.
    Apr 2008
    Thank You
    Thank you iraqveteran. I am a student as of right now and I needed some additional info for one of my classes.
    Dec 2003
    45th Parallel
    An "AXV" controls outlet pressure only. It does not care what the superheat is. The superheat on a AXV system is dependant on the load on evap coil.
    A "TXV" attempts to control superheat of evap coil by sensing suction line temp on outlet of Evap coil. As superheat increases, valve will be opened to allow more refrig into coil.
    An AXV valve has no sensing bulb, but a TXV does.
    Jan 2005
    steeler nation
    IV IV IX
    use your head for something other than a hat rack.......Gerry
    We have freedom because somebody fought for it.
    We keep it because we are willing to fight for it.
    We lose it because we are not willing to fight for it.