    HVAC run time

    Have 3 1/2 ton rheemn gas pack that runs 5 min off 17 min this has been average for the past 2 months i,ve been keeping track. Is this normal for such short run time" I,ve read its not good for short heat cycles

  2. #2
    Join Date
    Jan 2008
    Posts
    1,584
    You may be able to change the number of cycles per hour at the stat.
    Sounds like it may be set to 3 cph. Don't think you'ld want any less.
    Also sounds like your unit might be oversized.
    Just a guess.

  3. #3
    Join Date
    Apr 2004
    Posts
    7,680
    The unit produces a set btu per hour. It's running normal but may be oversized. You currently have 3 cycles per hour. Playing with the stat will probably not help. Leave it alone and next time they replace the HVAC system, make sure they do a load calculation.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,203
    Don't post the same question twice.