Thread: HVAC run time
-
03-30-2008, 12:57 PM #1
Regular Guest
- Join Date
- Jan 2007
- Posts
- 54
HVAC run time
Have 3 1/2 ton rheemn gas pack that runs 5 min off 17 min this has been average for the past 2 months i,ve been keeping track. Is this normal for such short run time" I,ve read its not good for short heat cycles
-
03-30-2008, 01:06 PM #2
You may be able to change the number of cycles per hour at the stat.
Sounds like it may be set to 3 cph. Don't think you'ld want any less.
Also sounds like your unit might be oversized.
Just a guess.
-
03-30-2008, 07:42 PM #3
The unit produces a set btu per hour. It's running normal but may be oversized. You currently have 3 cycles per hour. Playing with the stat will probably not help. Leave it alone and next time they replace the HVAC system, make sure they do a load calculation.
-
03-30-2008, 07:57 PM #4
Don't post the same question twice.