Size Hvac unit
Have a new 2044 sq ft heated brick home w/ tyvek wrap house that has 207 sq ft double pane low e windowws, 84 sq ft outside door space, 14' vaulted ceiling in 21' x 18 ft rm, 12 ' vaulted ceiling in 10' x 11' rm rest of ceiling 8' h . A 3 1/2 Rheemn RRNA-B042JK10E ton gas pack was installed heat 100,000 BTU and Cooling 42,000 btu. My problem is that the heat runs for about 5 min then off about 17 min. seems its always cold in the living room where the vaulted ceiling is.
Themostat was placed in the hall over the return duct where all the bedrooms are located. Should this be moved to the living room. I was told by the HVAC installer he could cap off something on the heat exchanger for less btu,s so it would run longer does this seem logical, or is unit just to big for house?
-
03-30-2008, 12:01 PM #2
Regular Guest
- Join Date
- Nov 2007
- Location
- Tucson AZ
- Posts
- 166
Fans
You need to mix the air in the living room - all your warm air is in a bubble at ceiling level.
A pair of ceiling fans blowing down should make a big difference. Moving the thermostat will just make other areas too hot, and while derating the furnace will make it run for longer periods. The only benefit from that will be better mixing of the air generally (which might help a little).
Focus on the living room where your problem is, and get the air there moving.
-
03-30-2008, 12:08 PM #3
Professional Member
- Join Date
- Aug 2005
- Posts
- 215
Do you have just 1 return air in the hall for the whole house?
The fans will help some, but how are the other rooms heating and cooling? are they to hot or cold?
-
03-30-2008, 12:15 PM #4
Regular Guest
- Join Date
- Jan 2007
- Posts
- 54
-
03-30-2008, 12:18 PM #5
Regular Guest
- Join Date
- Jan 2007
- Posts
- 54
Have one return in hall and one in master bedroom other rooms seem fine because only 8' ceiling w/exception of one bedroom with 12' Vaulted ceiling. Seems 3 1/2 unit to big had another house this size only 3 ton?
-
03-30-2008, 12:21 PM #6
Regular Guest
- Join Date
- Jan 2007
- Posts
- 54
Have one return in hall and one in master bedroom other rooms seem fine because only 8' ceiling w/exception of one bedroom with 12' Vaulted ceiling. Seems 3 1/2 unit to big had another house this size on
-
03-30-2008, 03:12 PM #7
Professional Member*
- Join Date
- Mar 2008
- Location
- Baltimore MD and Ridgebury PA
- Posts
- 542
Did the contractor perform a load calc (Manual J) when they sized and installed the system? On a related note, central returns are never as effective as individual returns for each room. That may not play a part in your problem but its not a good way to perform an install in a new home. Anyway, if they performed a proper load calc then either the supply to the living room is undersized or, as jeff520 stated, you need ceiling fans or some other method to push the warm air down from the ceiling.
-
03-30-2008, 07:49 PM #8
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,273
Increase the run time
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
03-30-2008, 07:55 PM #9
Did you have uneven room temps with the old unit.