Thread: I NEED SOME HELP YCD180 gas fired LOW HEAT ON A CHURCH

  1. #1
    Join Date
    Nov 2014
    Location
    MICHIGAN
    Posts
    38
    Post Likes

    Confused I NEED SOME HELP YCD180 gas fired LOW HEAT ON A CHURCH

    i need some help please i am at a job site emergency call low heat on a YCD180


    has a regular t stat installed and inducer has been replaced and the rtrm board also (not by me)

    someone available to help me PLEASE!!!!!

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    How do I help? You have told me nothing other than you need help with a possible heat problem.

  3. #3
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Have you the self test mode?

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    nevermind, open forum...

  5. #5
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Does "low heat" mean 1st stage only or would that be, low as in temperature of the space ?

  6. #6
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Replace the rest of the parts

  7. #7
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    Quote Originally Posted by Chuck View Post
    Replace the rest of the parts
    X2, there's only a couple left. Then you can find the crack in the u bend of the heat exchanger and put all those parts on the shelf for stock...

  8. #8
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    What's a regular tstat?

  9. #9
    Join Date
    Nov 2014
    Location
    MICHIGAN
    Posts
    38
    Post Likes
    Thread Starter
    ok i just got home (((((friggin cold))))) sorry i have been on this unit for a few hours ..... i will try to explain the best i can .......
    this unit has had issues for a long time (found this out about an hour ago 6:30pm est)
    they have had to reset this unit by cycling the power repeatedly to get it to work......sometimes once or twice....customer said lately(4mos) it has had to be reset 3-6 times to get it to heat.......

    3 weeks ago it began this issue of running producing low heat...........other people have worked on this unit and gave up ...... my company sent me on this and now it getting personal.....(i hate not figuring things out) i have info downloaded to diagnose but some of the info does not jive with what i see and i don't have experience on these microprocessor units........ can i get some info?????? i have run the self test and CFM does not change speed
    i had to change the ignitor ----- wouldnt sense flame.....green color hue visible on ignitor they said was changed 2 weeks ago

    now it runs ----- "low output" wont heat to full temp have never seen a code flashed unless i unhooked.... temp sensors

    there was a frequency modulator installed with 3relays(mars) and 1 contactor (these were removed by the last guy who worked on it.......

    the ingintion board was replaced -(cust said it was burnt)
    then the ignitor (both 6-7 weeks back)

    then the CFM was bad and replaced by another company

    the same guy removed the relays and F.M.

    i come along and it will not start correctly------now it runs ----runs----runs ---- does not satisfy temp


    i am real sorry but i am pulling my hair out on this ...... HELP and be patient please i am not a commerical trane tech but i am a residential tech Bryant/Amana

    so any body still here ????? i can answer as to WHAT I HAVE LOOKED AT AND TESTED but i am not at the unit presently........ thanks for reading.....Bill





    the ignition control board was

  10. #10
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Quote Originally Posted by rider77 View Post
    What's a regular tstat?
    Red/White/Yellow/Green

  11. #11
    Join Date
    Nov 2014
    Location
    MICHIGAN
    Posts
    38
    Post Likes
    Thread Starter
    R-W1-G-Y1-W2-Y2-C
    DOES NOT HAVE DIAG LIGHTS....as described in troubleshooting guide

  12. #12
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    How about a model number for starts ?

  13. #13
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Gas pressure

  14. #14
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Did you say combustion fan runs all the time?

  15. #15
    Join Date
    Nov 2014
    Location
    MICHIGAN
    Posts
    38
    Post Likes
    Thread Starter
    model #YCD180B3HOHB

    i found the bulletin on the CFM shorting out and it HAS NOT BEEN DONE.......

    8"wc SUPPLY SIDE
    ? unknown of CFM since its negative pressure..

  16. #16
    Join Date
    Nov 2014
    Location
    MICHIGAN
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by Chuck View Post
    Did you say combustion fan runs all the time?
    only when heat is energized

  17. #17
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Did both stages of heat run in test mode ?

  18. #18
    Join Date
    Nov 2014
    Location
    MICHIGAN
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Did both stages of heat run in test mode ?
    no i hear the relay click(on the board) but no change in CFM speed....

  19. #19
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    whats the pressure on the outlet side of the gas valve? what about the condition of the screen inside the burner where the ignitor is?

  20. #20
    Join Date
    Nov 2014
    Location
    MICHIGAN
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by chillerout1 View Post
    whats the pressure on the outlet side of the gas valve? what about the condition of the screen inside the burner where the ignitor is?
    the pressure is negative(0"WC) on outlet side and 8"wc supply side...... and the screen had about 20 holes plugged i cleaned that and no change

+ Reply to Thread
Page 1 of 6 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •